Answer / guest
May be the other side of the bus duct is grounded.........to
pass such a heavy current...........since it is already
grounded the buss duct offers very low resistance compared
to the human body.......
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / rupesh
as per my knowledge we will give a rated current of 2000a through low voltage high current source, not 415v. so the voltage is low then we will not get electric shock.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / t eswara rao
First thing, the input voltage of the testing kit will be
415V but not the output of the testing kit. Please check
this and confirm.
Second thing, As said by rupesh, rated amphere of 2000A
will be fed by fixed low voltage and variable High current
source. So, you will not get the shock.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jivan gangawane
Generally this test is carried-out to verify the temp limits.
The testing done by applying low voltage to one end and
other end is shorted by suitable link same as that of heat
run test we conduct on transformers.
the capacity of test transformer is limited. Primary voltage
is high but the voltage on the secondary is less to a few
volts to circulate SC current.
So due to low voltage of the source, cuurent thru your body
will not flow due to low voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shivakumara
Dear it's very low voltage generally 5.5 or 10volt will apply and for full load rating of busduct,
One more thing is that we will short 3 termilas or busbars in HEAR RUN TEST, due to that temperature will rise upto stabilizing we need to check accordingly with standards that you referring IEEE or IEC
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaarthikrt&c09894209497
if u ground that bus bar during testing then wat test wil u
conduct on that?if d bus bar gets 2000A v can realize a
heat but wat about tat 415V,i wil anser soon...
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / aks
1) The Test set up will be isolated from the source through
isolation (Two winding)testing transformers .The test set
up will be floating and there is no return path to the
source .So you will not get shock by touching at a single
point.
| Is This Answer Correct ? | 2 Yes | 3 No |
What are the types of class b amplifier?
what is the difference between static and dynamic induced emf?
14 Answers College School Exams Tests, MRF, Suraj Constructions,
What is Ohms law?
28 Answers College School Exams Tests, KPTCL, L&T,
WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SIZES??
14 Answers Dubai Group, Saudi Delta Groups, Savitha Electricals,
what is the reason of capacitor failure in alternator which is working with 10 kva dgset
how to calculate relay rating for 50kw load
what do u mean by knee point voltage?
Why alternators are rated in KVA?
What is the difference between multimeter
1. alternator has full load regulation of 4% when pf of the load is 0.8 lag, 1500 rpm. full load regulation of 1400 rpm for 0.8lag will be ________ ?? 2. torque angle of a sync m/c operating from a constt voltage bus is usually defined as space angle between _______ . 3. method most effective in finding out no load losses in large DC shunt motoris ______ . 4. current carrying capacity of fuse material depends on ______ . 5. coil has res. 10 ohm, inductance 1H. what wil be current after 0.1sec after switching on to a 500V DC SUPPL ? ? 6. effect of phase lag compensation on servo systems ___________ . 7. rotor of a dc machine is usually supported upon ______ . 8. DC motor is preferred to AC motor in which application ?? 9. 3 nos of 10:1 Xmer are connected in Star-Delta to supply a load at 230V.the supply voltage must be ______ . 10. voltage source produces max current in which circuit. 11. cal. power, if current and voltage are out of phase by 90 degree. 12. suitable length of Xmission line of power at 66 KV. 13. Which of the theorm helps in simple computation when the load across a ckt is varying ?? 14. what is the adopted line length for power Xmission of power by cables ??
why is the transmission voltage is multiple of 11?
I have 3 1000 kva single phase transformers and I wish to replace them with one three phase transformer. What is he kva rating of the new three phase, is it 1000 kva also or 3000 kva.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)