What is the role of P(Protional), I(Integral) and D
(Derivative) in PID Controller?
Answers were Sorted based on User's Feedback
Answer / arulnainar
1.P(Proportional): to calculate the error signal (Error
signal means the difference between Process variable(PV)and
Setpoint.(E=SP-PV)-- Present(Howmuch)
2.I(Integral): to remove the offset error. It will decide
howlong the error exist in the cycle.(Iitegral time in RPM
or MPR)--Past(HowLong)
3.D(derivative): It will decide how fast the control action
to remove the error without any overshooting or
undershooting in the process for future cycle.
For practically we can say Howmuch(present), Howlong(Past),
Howfast(Future) respectively P,I,& D.
| Is This Answer Correct ? | 39 Yes | 2 No |
Answer / abdus sattar mollah
lets us dscribe the role of indivitual |P,|I,|D in |PID
controller....
|P(proportonal)==to give one to one correspondense between
the error signal and manipulated signal.This give linearity
between the above two signal and thus bring output varialbe
to controlled value or set point.
|I(integral)==to remove the offset error.
|D(derivative)==to fasten the control action.
| Is This Answer Correct ? | 10 Yes | 1 No |
P(proptional):To control the present difference between sp
and pv
I(integral): To control the past
D(derivative) :To control the futcher
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / arpan singhania
PID controller.....
P is to attain the set point..
I is to remove the offset error..
D is to make the action fast and controllable..
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / www.islamqa.com
Actually we can make it simple:
# P:
it's a controller gain which modify the controller o/p
proportional to the error.
# I:
it's a controller gain which modify the controller o/p
proportional to the integral of the error.
# D:
it's a controller gain which modify the controller o/p
proportional to error rate of change.
We have 4 parameters in our control loop to focus on:
1 - the rise time: the period of time during which the pv
get 90% of the desired sp value
2 - max overshoot
3 - settling time: the period of time during which the pv
get the desired sp value and saturate.
4 - error/offset
we can get it clear from this pic:
http://controls.ame.nd.edu/ame437/S2003/hw1/specifications.j
pg
Now we will take a look about the effect of each controller
gain on these parameters:
# P gain:
decrease rise time
increase max.overshoot
increase settling time
decrease error (but not eliminate)
# I gain:
decrease rise time
increase max.overshoot
increase settling time
eliminate error.
# D gain:
no effect on rise time
decrease max.overshoot
decrease settling time
decrease error.
the previous is guidelines to be in background while
dealing with PID,but they are not sharp limits.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / panchal c.a.
Proportional- to control the offset between the process
variable and the set-point.
Integral- to control the time duration of the offset error.
Derivative- to control the rate of change of error.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / praveen kumar
P- means Offset remains
I- means removes the offset
D- means fast action,
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / chandra mohan
in PID controller
P controller used for reducing the over shoot,
I-controller used for reducing the offset,
D-controller used for reducing the ossilations
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / praveen kumar
p--> directly proportional to the process variable and give final element to fast action
i--> responds the error between process variable and setpoint
d-->rate of change of error with respective time.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is loop folder?
1 Answers Bapco Bahrain Petroleum Company, Hyundai,
What is the minmum distance between the electrical panel and Instrument panel
why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .
1 Answers Flour Tech Engineers (P) Ltd,
what will be the pressure in tank which has the total level of 2 meters and is filled 1.2 meters ?
what is the differnce betweeen hart and smart tx
what is the criteria to decide conductor size of a cable ?
a laways iface problem with brine level transmitter sealing diaphram a laways giving error and maximum reading i made re range and adjust with side glass but during commission it giving gap reading between it and side glass i need help from expert to explain how to calibrate it. note:dp transmitter yokogawa company
WHAT IS THE CAM POSITION IN CONTROL VALVE POSITIONER ? WHY IT IS USED?
I have energy meter for educational project having 0.5s class but my friend need 0.2s class meter , which one is good for that purpose and what is the actual difference of that two classes , need very easy example also.??
What are Sinking and Sourcing IO Cards
how to wire from pressure transmitter to marshalling panel and panel to controller and controller to dcs plz give the answer with example .
if drum level is low what is interlock? i mean we put interlock to fd fan or id fan ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)