Answer / arulnainar
1.P(Proportional): to calculate the error signal (Error
signal means the difference between Process variable(PV)and
Setpoint.(E=SP-PV)-- Present(Howmuch)
2.I(Integral): to remove the offset error. It will decide
howlong the error exist in the cycle.(Iitegral time in RPM
or MPR)--Past(HowLong)
3.D(derivative): It will decide how fast the control action
to remove the error without any overshooting or
undershooting in the process for future cycle.
For practically we can say Howmuch(present), Howlong(Past),
Howfast(Future) respectively P,I,& D.
| Is This Answer Correct ? | 39 Yes | 2 No |
Answer / abdus sattar mollah
lets us dscribe the role of indivitual |P,|I,|D in |PID
controller....
|P(proportonal)==to give one to one correspondense between
the error signal and manipulated signal.This give linearity
between the above two signal and thus bring output varialbe
to controlled value or set point.
|I(integral)==to remove the offset error.
|D(derivative)==to fasten the control action.
| Is This Answer Correct ? | 10 Yes | 1 No |
P(proptional):To control the present difference between sp
and pv
I(integral): To control the past
D(derivative) :To control the futcher
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / arpan singhania
PID controller.....
P is to attain the set point..
I is to remove the offset error..
D is to make the action fast and controllable..
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / www.islamqa.com
Actually we can make it simple:
# P:
it's a controller gain which modify the controller o/p
proportional to the error.
# I:
it's a controller gain which modify the controller o/p
proportional to the integral of the error.
# D:
it's a controller gain which modify the controller o/p
proportional to error rate of change.
We have 4 parameters in our control loop to focus on:
1 - the rise time: the period of time during which the pv
get 90% of the desired sp value
2 - max overshoot
3 - settling time: the period of time during which the pv
get the desired sp value and saturate.
4 - error/offset
we can get it clear from this pic:
http://controls.ame.nd.edu/ame437/S2003/hw1/specifications.j
pg
Now we will take a look about the effect of each controller
gain on these parameters:
# P gain:
decrease rise time
increase max.overshoot
increase settling time
decrease error (but not eliminate)
# I gain:
decrease rise time
increase max.overshoot
increase settling time
eliminate error.
# D gain:
no effect on rise time
decrease max.overshoot
decrease settling time
decrease error.
the previous is guidelines to be in background while
dealing with PID,but they are not sharp limits.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / panchal c.a.
Proportional- to control the offset between the process
variable and the set-point.
Integral- to control the time duration of the offset error.
Derivative- to control the rate of change of error.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / praveen kumar
P- means Offset remains
I- means removes the offset
D- means fast action,
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / chandra mohan
in PID controller
P controller used for reducing the over shoot,
I-controller used for reducing the offset,
D-controller used for reducing the ossilations
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / praveen kumar
p--> directly proportional to the process variable and give final element to fast action
i--> responds the error between process variable and setpoint
d-->rate of change of error with respective time.
| Is This Answer Correct ? | 0 Yes | 0 No |
why we are not using the turbine flow meter in the steam service?
What are the two program execution modes of PLC?
what is the procedure to isolate flow a transmitter and flushing it?
What is pre-commissioning and commissioning ?
PLZ explain to me massflow
How u will setup SPI(2007) on Citrix Server (Thin Client Mode)? Plz Justify?
what is the standard controll pressure
how to measure low temperature(<100 dec celsisus) with non condact sensor
What is the formula of vabration sesore. i mean how to covert mils to volt plz share if any body knows very argent : my mai is merajalam143545@yahoo.com
what is difference between modbus & fieldbus
For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?
what is the importance of CV in the control valves? how it is calculated?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)