WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS "
When the operation Download to HIS message appears:
Equalize start. HIS0163
WARNING: Could not connect to equalize destination. (7001)
Retrying. Number of retries = 0/1
ERROR: LdXopsLoadMain: connect error 10060
ERROR: LdXopsLoadMain: connect error 10060
ERROR: Processing terminated due to connection error. (7002)
Equalization end with errors. HIS0163
---- ERROR = 3 WARNING = 1 ----
Tell me, please, why and how to solve the problem."
Answers were Sorted based on User's Feedback
Answer / jigaranadkat
Dear Prasanth,
Please rest assured that your control network is good you
only have the problem in your open network. Thats the
reason that your plant functionality will not be affcted
but you can not download in to HIS0163.
Please follow the below procedure and let me know the
feedback...
1) Check the IP address of HIS0163. It should be :
172.17.01.63 and subnet mask : 255.255.0.0
2) Check for corruption of ethernet driver : (Right click
on my computer---> Go to device manager---> Check for
ethernet driver corruption).
3) Go to run.... Type CMD and give folling command...
ping 172.17.01.63... You should not face any dropped
package.
4) Go to run and type: \\172.17.01.63 or \\his0163
You should be exposed to common shared folder CS1000
5) Disable firewall in HIS0163.
7001/7002 is the code that your ENG STATION is not able to
find HIS0163 in the network.
* As a default setting, due to some group policy setting ..
Connection with blank password will be denied access. So
try to have a common administrative password for HIS0164
and HIS0163 and for operator USER NAME=CENTUM and PASSWORD=
CENTUM.
You may write your feedback to
anadkat.jigar@gmail.com
Hope this will resolve your problem.
Thanks & Regards,
Jigar Anadkat
Instrument Engineer
IBN RUSHD a SABIC affiliate.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / prashanth
thanks mr Jigar Anadkat
Instrument Engineer
IBN RUSHD a SABIC affiliate.
your suggession really helped
actualy firewall was turned on in HIS0163.
I TURNED OFF the fire wall and gave download,then it got
dowloaded successfully.
thank you
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthik
This means that HIS0163 is down and not connected to the
control network. Check Vnet/IP BUS1 and BUS2 connections and
the IP setting.
Once it's rectified , you should find HIS0163 in .SO (System
status overview).
Is This Answer Correct ? | 2 Yes | 2 No |
Dear Jigar Anadkat / Prashath,
This is the error.
Equalize start. HIS1145
WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1
ERROR: LdXopsLoadMain: connect error 10061
ERROR: Processing terminated due to connection error. (7002)
Equalization end with errors. HIS1145
---- ERROR = 2 WARNING = 1 ----
Regards,
John
Is This Answer Correct ? | 1 Yes | 1 No |
what is pneumatic control system?
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
how its work inductive proximity sensor explain briefly?
What is the three element? And how it work?
What are the two program execution modes of PLC?
what is the difference between CPC and i/p converter
What is Erosion in a control valve?
what is commisioning procedure,2)what is is the main work in commisioning in the field tx to dcs, plz send me detail
WHAT IS THE DIFFERENCE BETWEEN A TRANSMITTER & A SMART TRANSMITTER.
List three types Level Gauges with their working principles
what is the way of measuring air flow in air duct?explaim instruments used and DP creation in line?
what is the different between deflection type measurement and null type measurement in RTD?