how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula
Answers were Sorted based on User's Feedback
Considering Powe factor 0.8
Kw = KVA*.08
KW = 100*0.8
= 80 KW
w = 1.73 * 415 * Il * 0.8
80000 = 1.73 * 415 * I1 * 0.8
I = 80000/ 1.73*415*0.8
= 139 Amp
You can choose the cable which current carring capacity per
phase is on or above 140 Amp
By considering the future expansion of load the 180 Sq.mm
AYFY cable is ideal.
| Is This Answer Correct ? | 18 Yes | 2 No |
Answer / prashant singh
KVA=uder root3*V*A/1000
A=Under root 3*415*KVA/1000
| Is This Answer Correct ? | 22 Yes | 7 No |
Answer / abdulsubur
WE CAN GET FROM THIS REALTION
KVA=KW/KVAR
100*85=85KW
THEN FIND CURRNET FROM P=ROOT 3 VICOSPHI FORMULA THEN FIND
CURRENT AND THEN LENTH FROM THE MV=VD*1000/L*I
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / brijesh shakya
Before calculating size of cable, phase & voltage should be
clear then after we can calculate the current of load by
this formula
P=root3*V*I
I=P/(root3*V)
Accodingle we can select the size of cale.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / jack
Depends on what voltage you working with.
P = V*I
You got P and V, find what your I is.
Then use a cable selection book from, eg. Olex, choose your
cable from there.
| Is This Answer Correct ? | 7 Yes | 14 No |
Answer / jiwanjot
i think something is wrong with question ...load can never
be in KVA it should in kw if we talk about motor.....
| Is This Answer Correct ? | 5 Yes | 15 No |
Answer / mehul g. c.
if your load is single phase then you should use 3.5c x 185
sq.mm alu. Armoured cable.
| Is This Answer Correct ? | 1 Yes | 12 No |
Earth is a conductor or load?then ammeter connect to 3- phase supply,it shows the measurents or not?
What is STEP VOLTAGE ?
why transformer tank is in rectangular shape what happen when it is in step shape
i am having a 3 phase 12.5HP motor,that is connected in Star/delta.Without any Trip that motor stopped suddenly why?
how we can set the IDMT relay.
What is different between Difnit time and instatous over current relay
How do you maintain the earthing resistance?
13 Answers Birla, Ford, JLL,
which is the most advanced form of SF6 BREAKER?Can we use other gases to quench the arc?
What is burden of a current transformer. What is function of core in Transformer
1 Answers Jindal Steel and Power, NCC,
what is the meaning of DY-11 Z-5%
how to calculate energy meter multipling factor by ct & pt raitio
how much earthings are provided for 22KV HT Metering Kiosk
1 Answers GE, Gionee, Knight Frank, TATA, Vacmet,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)