Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula

Answers were Sorted based on User's Feedback



how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / virendra

Considering Powe factor 0.8
Kw = KVA*.08
KW = 100*0.8
= 80 KW
w = 1.73 * 415 * Il * 0.8
80000 = 1.73 * 415 * I1 * 0.8
I = 80000/ 1.73*415*0.8
= 139 Amp

You can choose the cable which current carring capacity per
phase is on or above 140 Amp

By considering the future expansion of load the 180 Sq.mm
AYFY cable is ideal.

Is This Answer Correct ?    18 Yes 2 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / prashant singh

KVA=uder root3*V*A/1000
A=Under root 3*415*KVA/1000

Is This Answer Correct ?    22 Yes 7 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / abdulsubur

WE CAN GET FROM THIS REALTION
KVA=KW/KVAR
100*85=85KW
THEN FIND CURRNET FROM P=ROOT 3 VICOSPHI FORMULA THEN FIND
CURRENT AND THEN LENTH FROM THE MV=VD*1000/L*I

Is This Answer Correct ?    11 Yes 6 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / brijesh shakya

Before calculating size of cable, phase & voltage should be
clear then after we can calculate the current of load by
this formula
P=root3*V*I
I=P/(root3*V)
Accodingle we can select the size of cale.

Is This Answer Correct ?    8 Yes 3 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / jack

Depends on what voltage you working with.

P = V*I

You got P and V, find what your I is.

Then use a cable selection book from, eg. Olex, choose your
cable from there.

Is This Answer Correct ?    7 Yes 14 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / jiwanjot

i think something is wrong with question ...load can never
be in KVA it should in kw if we talk about motor.....

Is This Answer Correct ?    5 Yes 15 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / mehul g. c.

if your load is single phase then you should use 3.5c x 185
sq.mm alu. Armoured cable.

Is This Answer Correct ?    1 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

Define branch?

0 Answers  


what is the problem in manufacturing transformer with 0 degree phase displacement.???why alwasys go for DYn11 or DY5?Whys not DY0 i.e zero degree displacement between primary and secondary side vectors?

3 Answers   Bhel, dpdc, Prime Electrical,


Difference between PLC and SCADA ? What are merits & De-merits of PLCs ? What are merits & De-merits of SCADAs ?

3 Answers   Ambuja,


Why silica gel use?

1 Answers   PWD,


Why we use a shunt capacitor or synchronizing Motor To Improve a Power factor pls reply me in this mail dinesh_elect_eng@yahoo.com

4 Answers  


Why generally the transformer primary is connected in star & secondary in delta

7 Answers  


plz send me the syllabus or any sample paper for engineer trainee recruitment if any,on ravinder911@yahoo.com

0 Answers   Bhel, Maruti Suzuki,


how the testing of CT OF 400/200/100 done in33/11 kv s/s

1 Answers   Reliance,


what's the requirement of Dy11d0 connection of 3 phase transformer?what's use of it?

0 Answers   Thermal Systems,


What is the maximun current carring capacity in per phase for three pole 100anps rating ncb

3 Answers   L&T,


where to use CT and PT?

4 Answers   CEB, Reliance,


10 tube light connect in mcb breaker.one tube light is fault.so breaker is tribe.how fault is rectified.(using 3wire phase,earth,neutral)

0 Answers   CTS, Jindal,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)