What will be the total current for 300kva UPS if it runs on
40 to 45 percent load. Is there any formula for to
calculate the exact load.
Answers were Sorted based on User's Feedback
Answer / pratheesh
We can calculate the total output current of a 300kva ups.
P=√3*V*I*CosΦ
Where P= Output power of UPS here 300000VA
V= Output voltage of UPS ( I hope this is a 3 phase
415 volts UPS)
I= Output current. (We need to calculate)
CosΦ= Powerfactor of the load. Varies depends the
nature of load(Inductive, Resistive or
Capacitive. We can assume this value is as 1
because we dont know the powerfactor, nature of
load.
So I= P/(√3*V*CosΦ)
= 300000/(1.73*415*1)=Approximately 420A per phase(if
the load distribution is balanced on each phase)
So, If the UPS runs on 40 to 45 percent load, it will take
around 170 to 190 Amps on each phase.
| Is This Answer Correct ? | 14 Yes | 8 No |
Answer / thowsif_emerson_csm team
For 300 KVA the Full load Current=KVA*PF,
i.e 300x.8=240000 Watts.
we know in 3 Phase Circuits,
P=1.732x V x I x Pf,
I=P/1.732xV x Pf,
I=240000/1.732 X 440 X 0.8,
Full Load Current, I =240000/609=394 Amps,
The Load Current @ 40% is 394*.40=158 A(Total Load Current).
The Load Current @ 45% is 394*.45=177 A(Total Load Current).
So load current at 40% Load is 39*.40=15.6 A/Phase Amps.
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / panindra polayadi
p=vI
where p for poore
v for vada
I for idippu
when we apply 40 to 45% load entteammo poore will blast
at that time vada will reduce idippu will be constant it is
newton,s fourth law after somedays newton,s fifth law will
be come beware
| Is This Answer Correct ? | 0 Yes | 4 No |
how we can do the insulation on secondary of ct explain and so that tan delta will within limit
what will happen when choke in tube light circuit was not working???
what sort of general awareness questions are asked in o.n.g.c entrance exam?????????????????
what is working of no & nc.
Difference between split ac and cassete ac?
what is the length of air terminal in lightening arrester system.
how system voltage affect the power factor or vice-versa.
what is per unit calculation?looking for simple and strong explanation thk u
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
HOW DO WE COLLECT THE SOLAR ENERGY AND DESCRIBE THE METHODS TO CONVERT THE SOLAR ENERGY INTO ELECTRICAL ENERGY?
what is settable hystersis protection? If any body knows plz kindly post the answer..
lllg,llg,ll,lg,lll which fault is severe and why?
10 Answers COEP, GE, PSC,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)