DEAR ALL
I have motors ( 10 units )each one is 90kw 380V 50 HZ 1000rpm
but new local pwer is 220v 60 hz
requierd rpm should be 1000
pleas what the beast solution is used frequncy converter or
rewinding all motos or chang all motors
thanks
Answers were Sorted based on User's Feedback
Answer / s.sakthivel perambalur
DEAR NOW AUTOMATIC FREQUENCY DRIVE AVAILABLE UPTO YOUR
REQUIREMENT (SIEMENS MAKE)
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shoeb
yuo need two cdevice one is auto transformer from which yuo
can adjust the voltage and other is cyclo converters whisc
can vary that 60hz frequency to 50 hz
| Is This Answer Correct ? | 3 Yes | 0 No |
VFD/ gear box is mandatory as 1000 rpm can not be the
synchronous speed with supply at 60Hz.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anjireddy boduggam
It is mandatory to install two devices:- 1) one device for
voltage adjustment 380v/220v 2)second device for HZ
Converter from 50hz/60hz, but as per technical knowledge
better to change them to suitable motors for 380 Volts / 50
HZ as the cost of Transformers (9nos.) and frequency
converters(50 HZ./60 HZ.) is more than the requirement.
| Is This Answer Correct ? | 0 Yes | 0 No |
The existing motors cannot be used. Voltage and frequency
is wrong.
The second issue is the speed - 1000 rpm uses a 6 pole
motor at 50Hz. 6 pole at 60Hz is 1200 rpm and 8 pole is 900
rpm.
You will need to change the voltage and frequency.
If the motors are belt drive changing the ratio of the
pulleys will fix the problem of speed.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k m sarafuzzaman
We Have to instolation A step up transfarmer.
| Is This Answer Correct ? | 1 Yes | 5 No |
Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?
how to calculate full load current of transformer & induction moter ?
What should be the dielectric strenght value of transformer oil of 11/0.433KV distribution transformer and 33/11KV tranmission transformer ?
Can any one know what are the symbols at the down (below) the analog ammeter??? there are 4 symbols which are they ?????
how to measure earth pit resistance
7 Answers BARC, BYD Electronic, Construction,
what will happen if ac power supply is given to the rotor of an alternator
hi friends ,iam working as genset AVR service engineer in electrical field from past 2 yrs throughout india . i plan to shift in some other job without travelling in same field because i con't travel,i dont know what i do for that so please guide me what job is suited for me,how i can serch the job please anybody helpme iam totally confused
After fault clearing in Tr line, whether the Metering core of CT is comes to normal condition from saturation region & its works as a normal condition?
Vibromotor 252MV 1/4HP2P..what is mean by 252MV?
what is the advantage of Cathodic eathing system and what is the basic principle and how itis working, please explain clearly .
In simply words(not explain any formula )what do you mean by power factor.?
Is there any rule to select the voltage of motor based on KW rating? What is the rating above which lt motor becomes the HT motor?.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)