Answer / sgthakur
Obviously ths is permissible.
1. carry on the PI test of each trans.It should not be less
than 2.00
2.Kva rating must be same
3 Percentage impdence must be same if diff .,parallaling
can be done but trans load shsring may be diff.
4 vector Gr.must be same
5If the Trans. HT source coming fr. diff. source, before
connecting them parallel phase ballancing and phase
seq.test must be done.
6.Other paralling condn. ie freq., voltage must be same as
usual.
7. On LT side trans. tape must be kept in same pos.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / manoj dubey
apart from above said pl. also check for your switchgear
rating for fault current as you parallel the system your
system fault current level will increase so your system
should be able to take care of it.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
It is permitted if you have individual self protected switch
gears for outgoing feeders
| Is This Answer Correct ? | 0 Yes | 0 No |
what will happen if i will done heart shape hole in transformer core?
can we choose current transformer secondary, to calculate residual flux in a power transformer, so as its saturation is close to the saturation level of power transformer?
what is the maximum load sutiable from earth to phase and what is the max voltage earth to phase suitable
Please sent me some previous year question papers of BSNL-JTO telecom and RRB in ELectrical Engineering to varshashahi@yahoo.com
What is mean by diversity Fator?
working of a diesel generator.
34 Answers ABC, AC, Cognizant, CTS, Directorate of Lighthouses and Lightships, KSL, Quippo, Shree Renuka Sugars, SRF, Svam Power, Tech Mahindra,
what is power factor for any engineering equipment?? what should be its value?
What is meant by power factor correction?
how can check the resistance of battery contact?
A resistance, inductance & capacitance are connected in series between points A & B.The voltage drops across the resistance,inductance&capacitance are found to be 40V,70V&100V respectively. What is the total voltage between between points A&B (Vab)? a)210V b)70V c)50V d)230V
what is the AC Plant and how can do the work with parts and picture tell us 150 Tr
Why we use CT on differant phases of 2ph.PT detection for brush-less static excitation of 3ph.,400v Synchronous Generator? What happen if use CT on same one of VT phase?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)