how to select cable size?
Answers were Sorted based on User's Feedback
Answer / brewed
There are many factors to consider when choosing cable
size .nd I will list just but a few.
1. You need to know the kind of load.
2. you need to know if its undergrond, overhead, in or out
doors
3. You need to know the temperature of your environment.
4. You need to consider the atmospheric pressure
With these and other facors you multiply them, depending on
your installation rules, to get a k factor which will then
depend on rated current carrying capacity of the cable at
hand.
Is This Answer Correct ? | 13 Yes | 4 No |
1.Voltage level.
2.Type of cable going to used.
3.Whether the cable is going to laid in air,tray or in
burried.
4.Derating factor, Grouping Factor and ambient temperature.
5.Voltage drop as per the standards.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / fida
I am using transformer turn ratio tester for 250KVA 13.8KV
primary and 220V secondary transformer what should be the
correct values of turn ratio test how i assume the correct
values for turn ratio.
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / leturtle
It is normal practice to have a rating for the earthing
system commensurate with the maximum system design fault
level. The normal maximum 400kV fault level is 63kA 1s.
Take the formula from EA TS 41-24 [6]
If you can't find it go to www.ees-group.co.uk on the FAQ
section.
Is This Answer Correct ? | 1 Yes | 4 No |
why r we using vaccuum circuit breakers in the place of m.o.c.b.
what is the significance of tan&delta and how it performed in power transformer
sir can you operated Transformer on frequency from that for which is design?
what is the differance between HT motors And LT MOTORS.
0 Answers Empire Vitrum Glass, Sappi,
why write 500v on line tester (Test pen)
Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?
v=I*R, i.e V is directly proportional to I. now P=V*I. so V=P/I. thus v is inversely proportional to I. so what is the correct one? If both are correct than for which kind of condition this 2 differ
How to connect the chemical earthing and complete process tell me plz
why reactor is connected before capacitor in APFC panel
what is the difference between concentrated winding and Distributed winding in motor?
how choose conductor &caple&wire depending upon the load
ELECTRICAL ENGINEER TEST IN FEWA ANY ONE HAVE KNOWLEDGE ABOUT THIS?????????