Write the formula for Fault MVA, Fault current, Base MVA.
Answers were Sorted based on User's Feedback
Answer / ariel
- Draw the per phase diagram of the system
- Express all impedance in per unit values
- Choose a common MVA base and express all Zpu on the
selected common MVA base
Znew= Zpu(MVA base/ MVA)
-Calculate the total per unit impedance of the system
using circuit principle
- Calculate the fault power
MVA fault= MVA base/ Z total per unit
I fault = MVA fault/ 1.73* V
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / mak
The fault current of a power transformer will depend on the following;
Transformer Rating (in KVA/MVA)
per unit impedence of the transformer (%p.u.)
line/phase Voltage (VL/VP)
the following formula can be used to find the fault current on the secondary side of a transformer
Fault Current = Transformer Rating /(per unit impedance x phase voltage)
The Values of Transformer Rating, per unit impedance & phase/line voltage will usually be mentioned on the transformer rating plate / data sheet
As an example a 500kVA, 11kV/400V/3-Phase/50Hz transformer with 5% p.u impendence will have the following fault levels on the secondary side
Fault level = 500/(5%)=10000kVA
Fault current = 500/(5% x 400 x 1.732) = 14.4 kA
Remember to use 3phase voltage!
| Is This Answer Correct ? | 3 Yes | 4 No |
what is transformer
63 Answers ABB, Advance Power Controls, CERC, Electrical, Electrical Supervisor Competency Certificate, ETA, IBM, Jindal,
What is cogging and crawling phenomenon in motor.
In LT cables 3.5 core cable are available that means 3 core and .5 for neutral Why .5 for neutral and is there any reason for that please suggest thanks and regards pavan kumar
what the Microsoft .NET framework is?
Transformer rating=> 15/20 MVA.Why there are two raings? What should be the rating of the fuse at the secondary if the voltage level is 13.8KV/4.16KV?
why only 11kv level is used for transmission purpose? why not 230v?
what is meant by vector group of a transformer? How can it be derived?
Rated moter voltage and frequency is 380volt 60 hz but moter is running at 380votac 50hz is this harmful for moter winding
how the BDV of the oil will be checked using moterised controled HV SET?
Do power transformers have an Automatic Voltage Regulator (AVR) just like the alternator/generator in a power system?
why in isolation transformer we dont get any shok?
what is bushing in transfermor
7 Answers Bokaro Steel, Visa Steel,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)