Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


hi this is noor in my work spot, i arranged THERMOCOUPLE in
the place of RTD. (in FEED WATER tank). can i use T/C or not?

Answers were Sorted based on User's Feedback



hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / pawan kumar

first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range. so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.

Is This Answer Correct ?    27 Yes 0 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / manash ranjan jena

You can use a Thermocouple in place of RTD but you need to
change your control loop instruments accordingly. As T/C
output will be mV where as RTD output is always change in
resistance. Please check the input of your measureing
instrument, if that is a universal input circuit then you
can use a T/C inplace of RTD.

Is This Answer Correct ?    20 Yes 2 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / manash ranjan jena

For feed water service the process temp. is always below
300 Deg. C. So you can very much use a RTD. And in lower
range RTD is a better solution than T/C. As it has a linear
curve and no compensation required. And even the accuracy
of RTD is better than T/C. However you can very much use a
T/C if the control network allows.

Is This Answer Correct ?    12 Yes 0 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / nn

yes, if thermocouple selection is suitable for the
operating temperature. Also you have to check if your
controller supports T/C signal or you have to had seperate
signal converter for that.

Is This Answer Correct ?    4 Yes 1 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / manraj

first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range (and also check type of i/p of
ur measuring instrument.) so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.

Is This Answer Correct ?    2 Yes 0 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / mjv

I M AGREE WITH ALL ABOVE ANS..BUT THE MAIN THING IS COST!!
RTD IS COSTLIER THAN T/C..

Is This Answer Correct ?    4 Yes 3 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / manish tyagi

No T/C are not suitable replaced for RTD because feed water
tank temperature below 120 Deg C (max.).T/C are right used
above 300 Deg C

Is This Answer Correct ?    2 Yes 4 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / praveen kumar

Yes u can use TC in the place of RTD, but check the
tempeatures range, again there a lot of things to see
whether Thermowell, suits the element or not.

Is This Answer Correct ?    1 Yes 4 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / n.h.ansari

no.

Is This Answer Correct ?    2 Yes 6 No

hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank)...

Answer / vishok

No. Because in RTD Resistance increases proportional to
temperature. But in thermocouple the output is voltage in
millivolts. So to process such signal you need pre
amplifier, and for RTD U need a bridge circuit.

Is This Answer Correct ?    4 Yes 11 No

Post New Answer

More Instrumentation Interview Questions

how works encoder in plc

0 Answers  


An atmospheric storage tank has a diameter of 20 m and a height of 8m.It is half-full of liquid with the remainder of the space containing air normally at atmospheric pressure. If the connection to atmosphere is accidentally closed off and 10 cubic m of liquid removed, what happens to the internal pressure of the tank? What are the possible consequences for the tank?

1 Answers  


in i/o panel for digital ouput(do) how much power(in volts) we must give?

2 Answers  


Which standard is used for calibration of Control Valves ?

2 Answers  


why we are using magnet for calibration of gas detector?

0 Answers   NSH,


What is Modbus communication

0 Answers  


what is commissioning & pre commissioning , explain with difination

2 Answers   Bapco Bahrain Petroleum Company, Shell,


Which is the best field foundation bus. ( FF ) Yokogawa, Honeywell or others ?

0 Answers   GNFC,


What inherent design and operating principles are included in a modern control system to use predictive maintenance practices to increase overall system reliability?

0 Answers  


wich is coming the first HAZOP OR SIL

0 Answers  


What is the differaence between PLC and DCS?

6 Answers  


What is paid how it works

0 Answers   KOC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)