hi this is noor in my work spot, i arranged THERMOCOUPLE in
the place of RTD. (in FEED WATER tank). can i use T/C or not?
Answers were Sorted based on User's Feedback
Answer / pawan kumar
first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range. so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.
Is This Answer Correct ? | 27 Yes | 0 No |
Answer / manash ranjan jena
You can use a Thermocouple in place of RTD but you need to
change your control loop instruments accordingly. As T/C
output will be mV where as RTD output is always change in
resistance. Please check the input of your measureing
instrument, if that is a universal input circuit then you
can use a T/C inplace of RTD.
Is This Answer Correct ? | 20 Yes | 2 No |
Answer / manash ranjan jena
For feed water service the process temp. is always below
300 Deg. C. So you can very much use a RTD. And in lower
range RTD is a better solution than T/C. As it has a linear
curve and no compensation required. And even the accuracy
of RTD is better than T/C. However you can very much use a
T/C if the control network allows.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / nn
yes, if thermocouple selection is suitable for the
operating temperature. Also you have to check if your
controller supports T/C signal or you have to had seperate
signal converter for that.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / manraj
first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range (and also check type of i/p of
ur measuring instrument.) so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mjv
I M AGREE WITH ALL ABOVE ANS..BUT THE MAIN THING IS COST!!
RTD IS COSTLIER THAN T/C..
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / manish tyagi
No T/C are not suitable replaced for RTD because feed water
tank temperature below 120 Deg C (max.).T/C are right used
above 300 Deg C
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / praveen kumar
Yes u can use TC in the place of RTD, but check the
tempeatures range, again there a lot of things to see
whether Thermowell, suits the element or not.
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vishok
No. Because in RTD Resistance increases proportional to
temperature. But in thermocouple the output is voltage in
millivolts. So to process such signal you need pre
amplifier, and for RTD U need a bridge circuit.
Is This Answer Correct ? | 4 Yes | 11 No |
In vortex flow meter how can measure the frequency of vortex generated by vortex flow meter
What is PID tunning
What s PDS & PDMS tools ?its role in instrumentation?
How many loops are there in the power plant? how many closed & open loop in the power plant ? Please give me the exact clarification?
how can we calibate ph meter. how can we calibrat conductivimeter how can we calibrat massflowmeter & it s working.
What are primary elements of measuring pressure?
We are used ABB 800xa 5.1.please tell me how to instrall this.
Hi Friends i need Electronics&Instrumentation Engg question papers for BARC written test by coming 20th May 2008 pls post ur use full info to kkumarei@gmail.com. Or for suggestions pls give one missed call to 9962122264
My flow transmitter range is 0-1000mmwc.DCS range is 0- 100m3/hr.What is correspond out put in terms of milliamps if my flow is 65m3/hr
what is the reason for flow fluctuations happen on differential flow transmitter during in service
What is MLFB number for Siemens?N How they are defined?Give me Answer with example like take any Signal module....
when an eddy current probe is installed inside of a turbine or compressor in case of probe problem same as:crash of head of probe,changing the scale factor because of low measuring gap(physical gap is ok(example=1.14mm)but voltage is reduced(example=-6 volts),is any way to check the probe,when the ohm of probe is ok.thank you,(Karim Tavakoli)