What power factor maintain you maintain at u r organisation
Answers were Sorted based on User's Feedback
yes the power factor in any organization should maintain from .8 to .99 or 1,
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / laxminarayan
In Industrial sector there are more inductive loads.The
inductive loads draws more load current.So maximum will be
the power factor less will be the load currnt.So power
factor should be maintained 0.97 to 0.99
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / ashish rai
It should be near to one(less than one) . but not to one.
For stability static device has come which control the
capacitor bank automatically. So there is no problem of
stability . If anyone are going for the small industry , he
should try to maintain it near to .95. .80 is not so
effective power factor now a days. It can be acceptable for
home application not for the industrial purpose.
Is This Answer Correct ? | 5 Yes | 2 No |
We maintain 0.8 and above since we are penalised by KEB for
low pf. we generally maintain close to 0.9 by use of power
capacitors. Too high i.e. above .95 is too costly to
install and also the problem is that if power factor is
close to 1 then there are chances of high voltage affects
motors and we suffer more motor burning at our plant.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sandeep lole
In industries, mostly the loads are inductive type. So the
PF is low near about 0.8 lagging. Due to that the load
current is maximum.We can improve the PF by using Capacitor
bank in industrial substation. So that we can improve Pf
upto 0.99. For that proper design of capacitor bank is
important.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / manish singla
I have always maintained Power Factor 1 (Not Leading Nor
Lagging) during my days with Maintenance Deptt.
Resulting in saving of Atleast Rs40k in monthly bills,
Better Voltage etc.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manish singla
In our state we get Incentive for maintaining Power Factor
over and above 0.90 Lagging till Unity.
Secondly, Maintaing Power Factor at Unity keeps your
distribution system healthy resulting in low line losses
within your premises as well inputs of your premises.
This is wrong statement that it will lead to burning of
equipments and premature failure of electrical equipment.
Is This Answer Correct ? | 0 Yes | 0 No |
Two electric lamps 40 W, 220 V each are connected in series across 220 V. What is the power consumed by the connection?
what is the function of choke in the flourcent tube lights and why the colour is in white mostly in flourcent tube lights
In 3phase supply Voltage will come around 370v then what will happen?(mean what will effect on electrical equipment like AC,UPS,Motors.)
what is meant by earth fault and how it happens....
What are the necessary components of the feedback control system?
how can decide the current rating of oltc
How much Fault current can be contributed by a motor?
what is the voltage and ampere rating of all range of HT conductor?
Define super node?
what is two point starter?
Does dry and oil transformers both require dedicated neutral, because in my project we are using 2500kv dry star delta transformer, where they say neutral not required and even it is not provided in our substation. can u let me know
I PURCHASED A DEISEL GENARATOR SET OF AVR TYPE& RATING 125KVA BUT SOME TIMES THE OUTPUT VOLTAGE IS FLUCTUATING WHAT ARE THE PROBABLE REASONS GIVE ME