HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I
DO MY SETTINGS FOR
OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP
FUNCTION IN MY 4000A CIRCUIT BREAKER?
Answer / k.prakashchandra
Set OCR at 110 % of rated current, ground fault at 10-20 %
of OCR,inst trip at 2 to 6 times the OCR and SC(inst) at 8
times the OCR.
Is This Answer Correct ? | 1 Yes | 0 No |
PLZ EXPLAIN CORONA,SKIN,BIRD PALE,SPAN,SAG Effects of power cable.
Why design 150Hz in Exciter
Why R ph of Hv and Lv is shorted or joined together while taking vector group?
Do you know the alignment of a motor?
Connection diagram for KW meter and Kva meter
What is mathematical model of a control system?
does not the circulating current in a transformer affect the flux distribution in the transformer core
how much amp MCB is required for 1/2 kva power back up?
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
what is Anti-pumping?
what is the significance of terminal voltage and phase sequence in the operation of paralleling of two generators?
Dear all, i completed M.E(Power Electronics & Drives) 2011 passed out having 78% so i need job in core side but i don't know how can i receive the calls from electrical companies and i uploaded my CV in naukri, times jobs etc.. In that iam not recieved any mails from good companies so give me best procedure plzzzzzzzzzzzzzzzzzzzzzzzz..... Thanks, K.Linga Reddy Email-id:-lingareddykmthm@gmail.com Ph no:-08015402078