What is the function of RCCB? What are the different sensitivity ratings & each application?..

Answer / s c budhiraja

RCCB means residual current circuit breaker. This is used
to trip the circuit in case of earth faults to prevent
electrical shocks.Different sensitivity ratings are
30ma,100 ma, 300 ma.These are used for Domestic, commercial
and Industrial electric loads respectively.

Is This Answer Correct ?    74 Yes 9 No

What is the function of RCCB? What are the different sensitivity ratings & each application?..

Answer / ravi

RCCB-Residual current circuit breaker.This is used in
Industrial safety purpose i.e. is to isolate the healthy
circuit whenever earth fault & overload current occurs.we
have in market at different type of ratings 30ma,100ma.as
per requirement will use above ratings.for example human
body having current flowing capacity of 30ma.so in
industrial as per safety constraint they will prefer 30ma
RCCB/ELCB.

Is This Answer Correct ?    27 Yes 11 No

What is the function of RCCB? What are the different sensitivity ratings & each application?..

Answer / sumit

residual current circuit breakern it works on a magnetic
current of circuit when circuit in healthy condition RCCB
works normaly but in any phase current going unbalance that
time RCCB will trip.because RCCB works on residual magnetic
current so unbalance current flows in relay & RCCB will
trip.

Is This Answer Correct ?    16 Yes 3 No

What is the function of RCCB? What are the different sensitivity ratings & each application?..

Answer / vikash kr jha

A residual current device (RCD), or residual current
circuit breaker (RCCB), is an electrical wiring device that
disconnects a circuit whenever it detects that the electric
current is not balanced between the phase ("hot") conductor
and the neutral conductor. Such an imbalance is sometimes
caused by current leakage through the body of a person who
is grounded and accidentally touching the energized part of
the circuit. A lethal shock can result from these
conditions; RCDs are designed to disconnect quickly enough
to mitigate the harm caused by such shocks.

Is This Answer Correct ?    11 Yes 1 No

What is the function of RCCB? What are the different sensitivity ratings & each application?..

Answer / jasmin

RCCB means residual current circuit breaker. This is used 
to trip the circuit in case of earth faults to prevent 
electrical shocks.Different sensitivity ratings are 
30ma,100 ma, 300 ma.These are used for Domestic, commercial 
and Industrial electric loads respectively. 

Is This Answer Correct ?    4 Yes 1 No

What is the function of RCCB? What are the different sensitivity ratings & each application?..

Answer / rishabh singh

RCCB is a electrical device which is called residual current circuit breaker. It prevent the human body from electrical shocks.whenever current is flowing through earth(E) & Neutral that time RCCB prevent human body.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Please brief working principle & construction of permanent magnet AC Servo motor

0 Answers   DRJ ARDE,


how to make a solar panel? why solar panel cell connected to serious?

1 Answers  


i have 500 amp inductive load of motors ,,,pleas tell me how can i calculate for capacitor bank for improving my power factor to 99 .....calcullations for capacitor bank,,,,

0 Answers  


What is the difference between relays and contactor construction wise?

0 Answers  


what is the preventing maintenance of transformer

1 Answers  






what is the use of reactive power

3 Answers  


how to find out 3 phase complex power in per unit in unbalanced system?

0 Answers  


what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?

0 Answers  


Why derating factor os applied on Cables?

0 Answers  


What is the difference between Isolator & Load Break Switch?

7 Answers   Infotech,


can u light up bulb with out useing neutral

12 Answers  


What is the minimum insulation value required for a cable between phase to phase and phase to earth of 380 Vac 50Hz circuit, having load arround 800 amps.

2 Answers   DEWA, TATA,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)