Answer / nitin bhoraokar , power plant
In delta - delta type winding connections,protection against
earth fault is difficult as zero sequence current will get
circulating in windings itself & will not flow to ground.
Hence transformer isolation on earth fault is
hectic.Stability against E/F will get lost.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / abc
Generally Transformer at generating station and at load
centres can not be used in delta-delta fashion due to non
availability of neutral point.
But if load is delta connected or in case of transmission
lines at both side then delta delta fashion can be used.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / subaharan
delta-delta transformers are using in high power required areas.power transmitting areas transformers,transformers parallel connection areas these type of transformers are used.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suhail a.
Because generally in transformers we need to get a neutral
point form the star that is what we r not using the delta to
delta.
| Is This Answer Correct ? | 2 Yes | 3 No |
WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?
how vfd drives energy save
WHAT IS THE DIFFERENCE BETWEEN RESISANTANCE AND IMPEDANCE IF IMPEDANCE IS MORE THAN RESISTANCE AT SAME VOLTAGE CAN WE HAVE RELATION DERIEVED BETWEEN THEM
How to check the cable fault / hv test of transformer cable.
What happen if transformer neutral path get removed ?
sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formula ?
what is the difference between control transformer and Potential transformer (PT)?
What is plc and how to do preventive maintenance
We have received supplies of the ordered material. payments against the supplies also released. Where ST paid 4% against form C. Meanwhile it has been observed that 25% of material supplied was defective. Please suggest whether the issuance of C form from our side would be stopped till settlement of liabilities.
What is the arc. I saw word arc in between sf6 & vcb brakers
our plant maximum demand has 500 kva.need to suggest me to maintained pf 0.98.how much capacitor bank will be connect to the supply line.
What are the functions of different probes used in cro?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)