Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

I am working on a 11KV system with fault current of 40KA
for 1 second. I have selected 2500MVA 11/0.433KV
transformer.
How can i find the impedance value for this transformer?
Please help me.

Answer Posted / kaushik

i don't understand the purpose of giving 1 second ......
but what i think solution will be
s.c mva=1.732*v*i.
s.c mva=1.732*11000*40000.
s.c mva=762.08 mva.
per unit impedence of the transformer will be= (base
mva)/(s.c mva)
taking transformer 2500kva(i think it is wrong 2500mva)
we get
=(2.5/762)*100=0.328% of tranformer impedence

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection

3825


how we design a pannel to start 10HP motor with the help of star delta starter?

2224


how oltc works in rectiformers of higher rating (27 mva,200v dc,120kamps) please provide me full information with diaggram.

2148


What is meant by Low Resistance Cable and High Resistance Cable.

1914


As we use capacitor bank in 3ph ckt to improve PF, can we use capacitor in single ph domestric use, in house we have Fan,Mixer,electric cooker,iron,tube choke they also lag the system,because it is inductive load. if it is possible to improve PF of single ph system-- if yes- type of capacitor to be used,connection diagram, working in detail. if no-- list it.

1782


Dear all, I just want to ask an expert on this forum for some insights. For the magnetic balance test, when applied voltage on a Delta-Star transformer e.g. Dyn11, the following relationships apply for HV side: 1.  H1-H2 = H2-H3 H3-H1 2.  H2-H3 = H3-H1 H1-H2 3.  H3-H1 = H1-H2 H2-H3 For the LV side also: 4.  X1-X0 = X2-X0 X3-X0 5.  X2-X0 = X3-X0 X1-X0 6.  X3-X0 = X1-X0 X2-X0 Is there a similar pattern for Y-d, Y-Y, D-d? And how about Y-z, D-z, Z-y transformers? I've tested a YNzn5 transformer and for LV side I don't see the pattern. In this particular case I got for LV side the following (see values below): H1-H0  H2-H0  H3-H0    X0-X1  X0-X2  X0-X3 128.0  119.9  7.2      29.2   13.3   15.8 70.7   128.4  59.2     23.4   22.0   3.6 7.2    120.1  128.1    13.4   29.3   15.8 What is the relationship here for LV? For row 1 I see the relationship, for row 3 I also see but it's shifted, but for row 2 I don't see such relationship. Any suggestions, answers, someone?

1876


What is touch potential and step potential?

2170


What is the voltage gain or transfer function of amplifier?

1144


what is the function of bearing in dc mchine" and where it is placed

2598


how to i get B licence,i am completed BE electircal and electronics engineering.i want to konw the proceduure to get b licence

1751


what is the difference between megger and earth resister ??

1819


why h parameter are called as hybrid parameter?

1982


Dear Respected sir how to test ABB REX521 protection relay by relay tester.

2749


Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing

1934


Explain in brief description about the operation of DG sets.

2453