Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why is it that the HT motors & motors having very low kW
rating(<1kW) have windings connected in STAR, whereas the
motors having in between kW ratings have DELTA connected
windings??

Answers were Sorted based on User's Feedback



why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / avdhesh

The basic differance in star and delta connection is that
in delta connection voltage across the winding is line
voltage (V-line) and in star connection it is phase voltage
(V-line/1.73). Same way current in each winding in delta
connection will be (I-line/1.73) and in star connection it
will be line current(I-line). Now to design any motor one
has to take cost of insulation as well as copper.In delta
connection you need higher insulation and in star
connection you need thick conductor to cary high current.

For HT motors current is less as voltage applied is high
hence to reduce insulation cost star connection is made.

For higher rating LT motors since current is high delta
configuration is recommonded.

If we do not follow above than cost and size of machine
willbe increase.
Hope this is the answer of your question.

Is This Answer Correct ?    6 Yes 0 No

why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / saurabh

During Design it self it is take in consideration
As Power = Torque x Angular Velocity(RPM)

So for same RPM(say 1500 rpm), for Same Input Voltage

1) In star connection Torque will be less hence Power
output will b less

2) In Delta Connection Toruqe will be More hence Power
output will b more

as far as HT motors are concern, in order to limit inrush
current star connection could b given.

Is This Answer Correct ?    6 Yes 3 No

why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / gunasekaran

that is not economical why we r going to high voltage for
high KW rating for reduce the loss. delta connected load is
giving 3 time power output than star.

Is This Answer Correct ?    3 Yes 0 No

why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / shyamal

Thanks Avdhesh for the answer...
Can you tell me whether one can operate star connected motors
with delta connection & vice versa?

Is This Answer Correct ?    1 Yes 0 No

why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / kanth.g

Actually the question is not in Proper way try to get it
right.

Is This Answer Correct ?    1 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

Difference between UPS and Inverter?

7 Answers   HCL,


Differentiate AC and Dc resistance

0 Answers  


quantizer means?

0 Answers  


Explain thin film resistors and wire-wound resistors

0 Answers  


how can we connect the capacitor bank to improve the power factor?

5 Answers  


On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall be the current rating of DC MCB ?

6 Answers   RR, TNEB Tamil Nadu Electricity Board,


Can you use a different size cable to complete a circuit if you run out what you are using?

2 Answers  


What is the difference between the watt hour meter and Var hour meter in terms of internal connection and work theory . ie "When the meter records watt-hour an when the meter records var hours ??"

13 Answers  


Which motor isused in indian railway system?

3 Answers  


Different between megger and contact resistance meter

3 Answers  


why we are using R,Y,B colours for 3 Phase ?

4 Answers   ITC Infotech,


What is the basic difference between 90% stator earth fault and 100% stator earth fault, and its phenmenona?

4 Answers   Reliance,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)