why the transformer secondary voltage is more than the load
end voltage like t/f 11KV/433V for 415V(terminal voltage)
Answers were Sorted based on User's Feedback
Answer / kapil
The regulation of transformer is same as it's percentage
impedance. this means the secondary voltage will drop @ 5%
for a transformer having 5% impedance. to compensate this
internal voltge drop we select nominal tap setting to 433
v. if you keep nominal tap for 415 V, we can not properly
utilize tapping range as 5% is internal drop at full load.
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / a.k.sen
To compensate the V-drop in the Transformer (considering Impedence value)at full load, Secondary voltage at 433V is selected for load terminal voltage at 415V.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vishvesh
this difference is kept between transformer secondary and
load terminal because. considering line losses (losses
occurs in the transmission line from transformer secondary
to load).there must be some voltage drop in the
transmission line and also c.t.and p.t. connected across
the line for protection relays also consumes some kind of
voltage from the line.
| Is This Answer Correct ? | 1 Yes | 4 No |
How to specific gravity of battery will check, i didnt saw any hydrometer. & say me how to dip into the battery what are the specifications are given in the hydrometer?
why we are giving D.C. supply to field of an alternator, why can't we give the a.C. supply
what factors to needed while selecting a MCB and MCCB
why we avoid parallel operation of diesl generator?
My energy meter ratio is -/110/root 3,1A and connected line CT is 100/1,PT is 11kv/110 so what is the MF for meter
What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr
What is meant by coupling capacitor?
Transfer function is == ? a. Mathematical model b. System with no physical structure c. Can be calculated through differential equations
Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?
what is ground clearence in transmission system.is it varies wit conductor size,height of poles,span.
define regulation
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)