what is the suitable voltage of transmission line to
transmit 10000w power through 250 km.
(a)11kv
(b)33kv
(c)66kv
(d)132kv
]and please tell me whats the logic behind it
Answers were Sorted based on User's Feedback
Answer / sunny maurya
I WILL SUGEST U TO PREFFER 66 kV LINES BECAUSE THE POWER TO BE TRANSMITTED IS NOT MUCH ,IS IN kW ONLY.logic behind this is that line losses r less at higher voltage, but u will think why not to use 132 kV lines ,It is because at higher voltage insulation cost increases,and cost of equipments as well.
| Is This Answer Correct ? | 13 Yes | 1 No |
Answer / nilesh chitalia
I prefare 132 KV for Transmit 10 KW because of high
distance, at high distance of transmission there is a high
loss of power in low voltage, otherwise the the diameter of
the conductor should be high and ultimately the cost of
conductor shall be high. So, It is better to transmit at
250 km, 132 KV is better.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / m thiyagarajan
Higher the voltage lower the voltage drop V=IR so 132kv
transmission is better
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / paridhi jain
132 kv because if high voltage is transmitted den volume of
conductor material req will be lesss n also losses will be less
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / paridhi jain
132 kv because if high voltage is transmitted den volume of
conductor material req will be lesss n also losses will be less
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / rod
The higher the voltage the greater the distance as the
current is less but the power is the same. For very long
distances DC at very high voltage is used.
| Is This Answer Correct ? | 1 Yes | 9 No |
How to calculate the ups battery back up? give the formula.
15 Answers Cushman Wakefield, Ethio Telecom, Exide, MacLellan, Morgan Stanley, TATA,
tan delta test of current transformer.
what is the difference between ground, earth and neutral?????????....
advantages & Disadvantages of Solar power system?
what is the current limit of lighting arrester ?
Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?
What is the meaning of burden and class of accuracy of CT?
what is meant by lagging & leading current
what precautions to be taken while desigining a LT,HT panel. Eg-LT panel PCC panel with ACB installed. HT panel VCB panel with VCB installed. & what is main diffrence betwn IP54 & IP55 construction of panel.
which motors is used in mixies
What is different between MCB & MCC & isolator switch
Difference between rating factor of cable and derating factor of cable?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)