Answer / moody
of course
when load pf is constant and the load current increase the
t.v decrease " lagging p.f"
at leading pf the t.v increasing
this occurs in synch generators
if the load is constant but the p.f changed or varried
the same operation happens in lagging , leading respectivly
thanks................
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / rahul
Yes it does.
Reactive loads ABSORB VARs. This may lead to deficit VARs
in the system causing VOLTAGE to GO DOWN.
( Note that EXCESS VAR___High VOltage
DEFICIT VAR___FAll in voltage)
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ritesh
yes, when reactive load is changed, the load power factor is
also changed. line current= active power/(voltage*pf),
therefore line current will also change for a constant load,
which will change the line voltage drop, therefore terminal
voltage will also get change.
| Is This Answer Correct ? | 1 Yes | 0 No |
Yes it will drop down vtg
increase in var can increase vtg
| Is This Answer Correct ? | 1 Yes | 0 No |
yes,
when reactance increase loss increase
so voltage decrease
| Is This Answer Correct ? | 5 Yes | 7 No |
In Panels Main Incomer considered should be TPN or FP?
what is ideal insulator. what are its parameter. Is poecelain insulator comes under this category.
Anybody now how to claculate the Bescom power consumption?
why tan delta test is carried out in the power transformer? which parameter are measure?
what is first pole to clear factor
What is a soft start?
It is used or not HT cable single core 630 sqmm in LT 3 phase capacitor bank which is used in PCC(power control center).
How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.
Sir, why generating power plant operating at above 0.9 lag? detail explaination?
Why auxiliary transformers are not connected in parallel in primary stations?
If symmetrical fault occurs at the terminal of a synchronous motor then how the motor will act...explain it..
what is the main parts of DG? how it is working?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)