We have 250 KVAR cacitor bank & our average load is 200kva
but our power factor is average 0.66 how can we maintane
it? how can we balance our load?

Answers were Sorted based on User's Feedback



We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.6..

Answer / joseph

It is better to express the `Load' in kW. In your case it
is assumed that the average load at a P.F. of 0.66 is about
132 kW. Please note that excessive capacitors in circuit
can act as `Load'. Hence, firstly ascertain whether the
Power Factor is 0.66 lag (lesser capacitors than required)
or 0.66 lead (more capacitors than required). The best way
is to switch off all the capacitors for some time and take
the P.F., kW, KVA readings from your meter. Based on this
suitable solution can be provided.

Is This Answer Correct ?    9 Yes 2 No

We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.6..

Answer / ashish

Consider your load in kw i.e 200*p.f.=200*.66=132kw
Generaly capacitor bank used for improving power factor
then by using this formula kw & kvar relation formula. it
will help u to decide exact kavar for ur load.

Is This Answer Correct ?    5 Yes 0 No

We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.6..

Answer / khalidshaikh

A CONSUMER HAVING TOTAL INSTALLED CAPACITY OR DEMAND UP TO
200 KVA. THE CONSUMER ARRANGED 250 KVAR CAPACTOR BANK, I
THINK CONSUMER IS MISS GUIDED OR HIS CONNECTION POINT IS AT
FOR DISTANCE FROM THE SUPPLY SOURCE, WHERE HE RECEIVE
DROPED VOLTAGE AND HIS LOAD IS TOTALLY INDUCTIVE WHICH
DECREASES POWER FACTOR. OR LEADING POWER FACTOR WHICH
CAUSES ALSO LINE LOSSES.
IT IS SUGGESTED THAT CONSUMER GOT INSTALL KVARH METER AND
KWH METER WITHOUT CAPACITOR BANK IN CIRCUIT THAN AFTER A
CERTAIN OBSERVATION TIME GOT CALCULAT POWER FACOR AND
ARRANGE FOR THE REQUIRED VALUE CAPACITOR BANK.
THANKS

Is This Answer Correct ?    4 Yes 1 No

We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.6..

Answer / zahid noor

Connecting a capacitor bank to laod is not sufficient to
control power factor, it is controlled by increasing &
decreasing value of capacitor on increase & decrease of
your load, which needs to be calculated & automatic control
can be given by APFC panels. Please contact a suitable
party .

Is This Answer Correct ?    3 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

A synchronous motor is operating at a leading power factor .if the applied voltage is decreases ,(the excitation remains constant ) ,the motor current a)increases b) decreases c)remains same d) none of these

2 Answers  


What is the relation between the Peripheral speed(N) , no.of poles(P) and diameter(D) of a cylindrical rotor alternator ?

5 Answers   NTPC,


Write the analogous electrical elements in force voltage analogy for the elements of mechanical translational system.

0 Answers  


Supose we have one 220v A.C fan.if we provide 220v D.C what will be happen?

13 Answers  


Why electric sock occur to human or any lives ?

2 Answers  






The mechanical angle is electrical angle A always less than B greater than or equal to C equal to D less than or eaual to

1 Answers  


Any one who apply for Ferro Scrap Nigam Limited cn join with me at rajuhalder@indiatimes.com or 09669717028

0 Answers   SSS,


How to calculate that clean water supply in one Day from 150 KLD STP?

0 Answers  


what do w do when the output of generator is fluctuating?

0 Answers  


If the positive terminal of batteries in 125 v dc system is connected to earth what will happen ?

4 Answers  


how many units consumed by 8.5 ton ductable split ac in one hour in 3 phase?

2 Answers   Servis,


What is the power rate of power transformer?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)