We have 250 KVAR cacitor bank & our average load is 200kva
but our power factor is average 0.66 how can we maintane
it? how can we balance our load?
Answers were Sorted based on User's Feedback
Answer / joseph
It is better to express the `Load' in kW. In your case it
is assumed that the average load at a P.F. of 0.66 is about
132 kW. Please note that excessive capacitors in circuit
can act as `Load'. Hence, firstly ascertain whether the
Power Factor is 0.66 lag (lesser capacitors than required)
or 0.66 lead (more capacitors than required). The best way
is to switch off all the capacitors for some time and take
the P.F., kW, KVA readings from your meter. Based on this
suitable solution can be provided.
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / ashish
Consider your load in kw i.e 200*p.f.=200*.66=132kw
Generaly capacitor bank used for improving power factor
then by using this formula kw & kvar relation formula. it
will help u to decide exact kavar for ur load.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / khalidshaikh
A CONSUMER HAVING TOTAL INSTALLED CAPACITY OR DEMAND UP TO
200 KVA. THE CONSUMER ARRANGED 250 KVAR CAPACTOR BANK, I
THINK CONSUMER IS MISS GUIDED OR HIS CONNECTION POINT IS AT
FOR DISTANCE FROM THE SUPPLY SOURCE, WHERE HE RECEIVE
DROPED VOLTAGE AND HIS LOAD IS TOTALLY INDUCTIVE WHICH
DECREASES POWER FACTOR. OR LEADING POWER FACTOR WHICH
CAUSES ALSO LINE LOSSES.
IT IS SUGGESTED THAT CONSUMER GOT INSTALL KVARH METER AND
KWH METER WITHOUT CAPACITOR BANK IN CIRCUIT THAN AFTER A
CERTAIN OBSERVATION TIME GOT CALCULAT POWER FACOR AND
ARRANGE FOR THE REQUIRED VALUE CAPACITOR BANK.
THANKS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / zahid noor
Connecting a capacitor bank to laod is not sufficient to
control power factor, it is controlled by increasing &
decreasing value of capacitor on increase & decrease of
your load, which needs to be calculated & automatic control
can be given by APFC panels. Please contact a suitable
party .
| Is This Answer Correct ? | 3 Yes | 2 No |
125Kva Dg can take up how much amphere load.
What happen if two protection core (3p) of VT in LAVT are 11kv/root3, 110v/root3 and one protection core (3p) is 11kv/root3, 110v/3
How to calulate cable size for 200KVA,160KVA& 40KVA load?
In supply RYB are mentioned. But in transformers, why they are mentioning XYZ?
Unit of Magnetic Flux Density a) Tesla b) weber c) Hendry d) Farad
which type of motor is suitable for water pump?
what type of cables exsisting in the world and how many types
DESCRIBEPNEUMATIC SYSTM OF ASH HANDLING PLANT
HOW TO MEASSURED THE AMPS RATING FOR SUITABLE CABLE SIZE?
what is surge voltage and surge current?
Can a generator rated 400 V, 60 Hz be used in a 50 Hz System? Yes or No ? Why ?
what is the use of sdf?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)