We have 250 KVAR cacitor bank & our average load is 200kva
but our power factor is average 0.66 how can we maintane
it? how can we balance our load?
Answers were Sorted based on User's Feedback
Answer / joseph
It is better to express the `Load' in kW. In your case it
is assumed that the average load at a P.F. of 0.66 is about
132 kW. Please note that excessive capacitors in circuit
can act as `Load'. Hence, firstly ascertain whether the
Power Factor is 0.66 lag (lesser capacitors than required)
or 0.66 lead (more capacitors than required). The best way
is to switch off all the capacitors for some time and take
the P.F., kW, KVA readings from your meter. Based on this
suitable solution can be provided.
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / ashish
Consider your load in kw i.e 200*p.f.=200*.66=132kw
Generaly capacitor bank used for improving power factor
then by using this formula kw & kvar relation formula. it
will help u to decide exact kavar for ur load.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / khalidshaikh
A CONSUMER HAVING TOTAL INSTALLED CAPACITY OR DEMAND UP TO
200 KVA. THE CONSUMER ARRANGED 250 KVAR CAPACTOR BANK, I
THINK CONSUMER IS MISS GUIDED OR HIS CONNECTION POINT IS AT
FOR DISTANCE FROM THE SUPPLY SOURCE, WHERE HE RECEIVE
DROPED VOLTAGE AND HIS LOAD IS TOTALLY INDUCTIVE WHICH
DECREASES POWER FACTOR. OR LEADING POWER FACTOR WHICH
CAUSES ALSO LINE LOSSES.
IT IS SUGGESTED THAT CONSUMER GOT INSTALL KVARH METER AND
KWH METER WITHOUT CAPACITOR BANK IN CIRCUIT THAN AFTER A
CERTAIN OBSERVATION TIME GOT CALCULAT POWER FACOR AND
ARRANGE FOR THE REQUIRED VALUE CAPACITOR BANK.
THANKS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / zahid noor
Connecting a capacitor bank to laod is not sufficient to
control power factor, it is controlled by increasing &
decreasing value of capacitor on increase & decrease of
your load, which needs to be calculated & automatic control
can be given by APFC panels. Please contact a suitable
party .
| Is This Answer Correct ? | 3 Yes | 2 No |
Why dose an electric meter record KVA when there is no load on a 500 KVA transformer
How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?
How can we have to decided motor connection as a STAR-DELTA or DELTA-STAR?
if one of the phase is failed to 3 phase IM. what will happen?
what is ripple ??? what is harmonics ?
As we know that during saturation test of CT from secondary side, the current in secondary shoots up after core saturation. How core saturation effects the secondary current?
How to minimize the eddy current losses?
what is the differences between single phase ind. motor and three phase ind.motor?
how to copy from plc ge fanuc versamax series,all input and output, adress, and printout.
and gate circuit diagram,amplifier circuit diagram
if a 3 phase induction stator has charactristic plate and have on winding inside.with the calculation of plate or dimenssion of core how one can desinge rewinding drawing.
what is rms value?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)