We have 250 KVAR cacitor bank & our average load is 200kva
but our power factor is average 0.66 how can we maintane
it? how can we balance our load?
Answers were Sorted based on User's Feedback
Answer / joseph
It is better to express the `Load' in kW. In your case it
is assumed that the average load at a P.F. of 0.66 is about
132 kW. Please note that excessive capacitors in circuit
can act as `Load'. Hence, firstly ascertain whether the
Power Factor is 0.66 lag (lesser capacitors than required)
or 0.66 lead (more capacitors than required). The best way
is to switch off all the capacitors for some time and take
the P.F., kW, KVA readings from your meter. Based on this
suitable solution can be provided.
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / ashish
Consider your load in kw i.e 200*p.f.=200*.66=132kw
Generaly capacitor bank used for improving power factor
then by using this formula kw & kvar relation formula. it
will help u to decide exact kavar for ur load.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / khalidshaikh
A CONSUMER HAVING TOTAL INSTALLED CAPACITY OR DEMAND UP TO
200 KVA. THE CONSUMER ARRANGED 250 KVAR CAPACTOR BANK, I
THINK CONSUMER IS MISS GUIDED OR HIS CONNECTION POINT IS AT
FOR DISTANCE FROM THE SUPPLY SOURCE, WHERE HE RECEIVE
DROPED VOLTAGE AND HIS LOAD IS TOTALLY INDUCTIVE WHICH
DECREASES POWER FACTOR. OR LEADING POWER FACTOR WHICH
CAUSES ALSO LINE LOSSES.
IT IS SUGGESTED THAT CONSUMER GOT INSTALL KVARH METER AND
KWH METER WITHOUT CAPACITOR BANK IN CIRCUIT THAN AFTER A
CERTAIN OBSERVATION TIME GOT CALCULAT POWER FACOR AND
ARRANGE FOR THE REQUIRED VALUE CAPACITOR BANK.
THANKS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / zahid noor
Connecting a capacitor bank to laod is not sufficient to
control power factor, it is controlled by increasing &
decreasing value of capacitor on increase & decrease of
your load, which needs to be calculated & automatic control
can be given by APFC panels. Please contact a suitable
party .
| Is This Answer Correct ? | 3 Yes | 2 No |
How to calculate energy stored in a capacitance
what r the advantage of selecting micro controller type tripping of circuit breaker than relay type tripping?
WHAT IS THE difference betwwen LT CABLE AND CONTROL CABLE
Difference between Lugs and Thimbles
what is the difference between the alternator used in hydro and thermal power plants??
WHEN SINGLE PHASE SUPPLY AS 220V, WHY THE 3 PHASE- 4 WIRE MEASURED AS 440 VOLTS INSTEAD OF 660 VOLTS (220 VOLTS PER PHASE i.e 220x3 = 660 volts ).
Hello seniors m an engineering student in 3rd yr..i want to know what are the software course in electrical field?i wanted to do certification course but i dont know much about the course?..Regards
while calculating demand in my company the present load in kw is 212.... there 125kvar capacitor bank is installed by spliting as 50 in departments...the diasplay in panek biard shows 175kw... how could we know the amount of kvar used to compensate the kva
HOW DOES THE FAN REGULATOR CONTROLS ITS SPEED
29 Which of the following breaking method save energy? A regenerative breaking B plugging C dynamic breaking D none of above
how does grading rings & spacers in transmission line works? Working Principle?
help me with the question that might be ask on the interview for technical position
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)