why we are using panel space heaters in different control
schemes????
Answers were Sorted based on User's Feedback
Answer / abhishek
panel space heater is used for removing the moisture due to
which insulation breakdown may occur
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ilononurb
panel space heater is used to drying up the moisture
entered in the panel to avoid surface leakage current which
may affect the insulation dielectric strenght of the
insulator failure that may cause of series and shunt fault
in the system.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / xyz
PANEL SPACE HEATERS ARE NOT A MUST THESE ARE GENERALLY
PROVIDED IN EUROPEAN COUNTRIES AS THIER CLIMATE IS VERY
COLD AS COMPARED TO OURS.BUT AS WE ARE INDIANS WE BLINDELY
TEND TO FOLLOW THERE CONFIGURATION AND SO WE DO........EVEN
IF NOT NECCESORY AND THATS WHY THIS WAS ASKED............
| Is This Answer Correct ? | 2 Yes | 0 No |
WHAT IS counter flux IN CT?
What is an iron loss or core loss pi?
In a circuit a capacitor (paper capacitor ) was burned due to over voltage in this case can we replace that type cappacitor with other tye capacitor ?
WHY SEPARATELY EXCITED MACHINE NEEDS EXCITATION BY DC SUPPLY WHY NOT BY AC
what is the difference b/w permitivity and permeability
What does a Bode plot tell you?
What is it mean Transformer 100/133MVA Power Transformer, significance of 100/133 MVA and 230/115KV please
What is the Ohms low calculation
What is PEC??Applications........
How earthing of switchgear system to be done.
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
what is the ambient temperature of transformer oil & winding?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)