Answer / rakesh thakur
HI-pot test is use to test the insulation breakage of
various electrical auxilaries like cables,switchgears
etc.A HI-POT is a autotransformer which produces high
voltage of the desired level of testing, like for 33kv
system we will increase the output voltage of HI-POT slowly-
2 from o to 33 kv and apply it across the testing specimen.
If insulation of the specimen is all right than there will
be zero lekage current(meter affixed on HI-POT) and if
there is any insulation breakage in the system than there
will be certain value of leakage current on certain value
of value of voltage and circuit will got tripped.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / asif
Dear tech,
because of this test you can know well of your equipment
insulation strength and conductor strength.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kanagasabai
HI-pot is High pontential test(or) High voltage test.
Many people are familiar with a continuity test. A
continuity test checks for "good connections." You do a
continuity test by seeing if current will flow from one
point to another point. If current flows easily enough then
the points are connected. Many people aren't familiar with
a hipot test. "Hipot" is short for high potential (high
voltage). A hipot test checks for "good isolation." You do
a hipot test by making sure no current will flow from one
point to another point. In some ways a hipot test is the
opposite of a continuity test.
Continuity Test: "Make sure current flows easily from one
point to another point."
Hipot Test: "Make sure current won't flow from one point to
another point (and turn up the voltage really high just
make sure no current will flow)."
In the simple case a hipot test takes two conductors that
should be isolated and applies a very high voltage between
the conductors. The current that flows is watched
carefully. Ideally not much current will flow. If too much
current flows the points are not well isolated and they
should fail the test.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / karthik
Hi-Pot test (High Potential) test is used to find out the
insulation strength of a conductor.Usually a voltage of 125%
of rated voltage is applied during the initial test of the
insulation.For any future tests(which should not be carried
out)the applied voltage is less than 100% for not degrading
the insulation.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheik
this test you can know well of your equipment
insulation strength and conductor strength
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / aeccsrpudur
sir
its a high potential test
normally this test is conducted for cables and generator windings
for example if the cable is rated for 11kv and it should with stand 1.25 times of rated voltage during surge conditions
procedure for test - apply dc high voltage 1.25 times gradually and noted the leakage current ,it should be below 100 micro amps for healthy cable for 1 minute
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the knee point voltage in current transformer
How many battery required for an 3kva online ups with 3 hrs back up with usage of 3 fans,3tube lights
Why fuel tanks to be earthed ?
6 Answers Electronics, Hindustan Petroleum, HPCL, Ispat,
for what purpose the star point is done in ct
what is first pole to clear factor
how can we calculate the ampacity of the electrical wire/cable. and what are the factors must be considered. pls. elaborate.
what is the merz prodution ? what is the turn to turn fault?
what is the most probable reason of failure of current transformer?
I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current 36 A,but wenn i put load after 2 hours the current increase more than 156 A. Can anybode tell me waht is the Problem?
Whether capacitor loads can be connected for testing a diesel engine at its full load capacity? Is there any limitation of capacotir load? Which is the best load for testing DG sets?
What is mean by CT Saturate? how do we calculate?
you have a 2 tonne ac that operates for 2 hrs daily what will be you monthly bill (this is complete question asked nothing else was given)?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)