Can any body tell me about Hi-pot test, and why it is
necessary and its procedure of testing
Answers were Sorted based on User's Feedback
Answer / rakesh thakur
HI-pot test is use to test the insulation breakage of
various electrical auxilaries like cables,switchgears
etc.A HI-POT is a autotransformer which produces high
voltage of the desired level of testing, like for 33kv
system we will increase the output voltage of HI-POT slowly-
2 from o to 33 kv and apply it across the testing specimen.
If insulation of the specimen is all right than there will
be zero lekage current(meter affixed on HI-POT) and if
there is any insulation breakage in the system than there
will be certain value of leakage current on certain value
of value of voltage and circuit will got tripped.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / asif
Dear tech,
because of this test you can know well of your equipment
insulation strength and conductor strength.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kanagasabai
HI-pot is High pontential test(or) High voltage test.
Many people are familiar with a continuity test. A
continuity test checks for "good connections." You do a
continuity test by seeing if current will flow from one
point to another point. If current flows easily enough then
the points are connected. Many people aren't familiar with
a hipot test. "Hipot" is short for high potential (high
voltage). A hipot test checks for "good isolation." You do
a hipot test by making sure no current will flow from one
point to another point. In some ways a hipot test is the
opposite of a continuity test.
Continuity Test: "Make sure current flows easily from one
point to another point."
Hipot Test: "Make sure current won't flow from one point to
another point (and turn up the voltage really high just
make sure no current will flow)."
In the simple case a hipot test takes two conductors that
should be isolated and applies a very high voltage between
the conductors. The current that flows is watched
carefully. Ideally not much current will flow. If too much
current flows the points are not well isolated and they
should fail the test.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / karthik
Hi-Pot test (High Potential) test is used to find out the
insulation strength of a conductor.Usually a voltage of 125%
of rated voltage is applied during the initial test of the
insulation.For any future tests(which should not be carried
out)the applied voltage is less than 100% for not degrading
the insulation.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheik
this test you can know well of your equipment
insulation strength and conductor strength
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / aeccsrpudur
sir
its a high potential test
normally this test is conducted for cables and generator windings
for example if the cable is rated for 11kv and it should with stand 1.25 times of rated voltage during surge conditions
procedure for test - apply dc high voltage 1.25 times gradually and noted the leakage current ,it should be below 100 micro amps for healthy cable for 1 minute
| Is This Answer Correct ? | 0 Yes | 0 No |
For 1 KVA load how much KVARH capacitor can be used ?
3 Answers NLC, TNEB Tamil Nadu Electricity Board,
How to calculate voltage drop loss in HT 11000 Volts XLPE Aluminium conductor cable. Any specific formula or Thumb rule
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
Advantage of 11KV ring main system with open point
1 Answers Alam Group of Companies,
what is the spdt
Do closed loop systems require manual input?
DESCRIBEPNEUMATIC SYSTM OF ASH HANDLING PLANT
Why the earth to phase voltage is high 250 compare to other two phases
What is the speed of electrical supply?
Generally in AC we consider voltage, frequency and phase sequence for parallel operation ... Can we parallel two DC battery chargers? If yes, then what precaution to be taken when we parallel two DC power?
Why there is not any reactive power in DC although it causes magnetic field.
What is the unit of attenuation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)