Assume a condition such that two motors of rating
6.6kv,415v are connected to blower,so tell me which motor
draw large current give appropriate reason?
Answers were Sorted based on User's Feedback
Answer / pillay
The current drawn depends on the power consumed by the motor
and the operating voltage.
KW =1.72 X VL X IL X PF
Now assuming both the motors are loaded at 100 kw each OF PF
0.8 than the 6.6kv motors current consumption will be
100000KW /1.72 X 6600 X 0.8 =11 AMPS
If 415 volts is used than
100000 / 1.72 x 415 x 0.8 = 175 AMPS.
Is This Answer Correct ? | 17 Yes | 1 No |
Compare salient pole and Hndrical rotor machines.
what is differance between dirty earthing and clean earthing and their applications
during the period of armature reaction ,if the brush shift is not accomplish, what happen?
is there or does RCCB work for single phase connection?
The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machine which has to be installed where neutral to earth is not shorted and shows a leak voltage <3 Volts. Please suggest me how it is possible.
which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection
What will happen if 2 phase supply is given to 3 phase motor?
what is difference b/w bus duct & bus bar.
what is spill current?
What is different between Metering CTs and Protection CTs?
What are test values for an 63 KVA and 100 Kva Distribution Transformers for the following typical tests 1)Magnetic balance 2)Short circuit test 3)Open Circuit test 4)Vector group confirmation test .please give me the standard values for all the above tests.
Why primary batteries not rechargeable and secondary batteries are rechargeble??? If any one know please send me.