what is diffential relay? testing proceure?and
transformer reach Over load thet time differencilal relay
operate or not ?
Answer Posted / g.govarthinam
Dear friends
1.Diff relay compares two currents entering and leaving the
protected equipment or zone in respect of current
maagnitude and phase angle, and if there is any unbalance
or spill current found, that current will flow through the
operating coil of the relay and give trip pulse to the
Circuit breaker to isolate the supply to the transformer.
2.Please note that,Diff relay will operate only for
internal fault of the protected equipment(for
example,winding fault in transformer) and it should not
trip for over load of transformer and any external fault.
please feel free to ask further doubts in this topic.
regards
gova
| Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
why in a swquence network representation, the negetive sequence generated voltage is taken as zero?
determine two methods to find loose connection in operational electrical system?
In Power cable specification what is U0/U and Um.
How to select the cable and voltage drop in circuit?
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
how braking & making capacity of circuit breaker is calculated?
How DC earth leakage currents can be reduced ?
impliment (AB)`+C to transistor representation
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
technically, what is the reason behind starting the motor star the delta connection .. and what other ways to do this rather than using " star-delta transformer"
When we connect the large capacitor bank in series ?
how to test and calculat the head and discharge in borewell compressor
How to calculate ant test the burden of Current transformer
how will we calculate the copper wire load..
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is