why mccb is not tripping when phase & neutral terminal are
interched ?
Answers were Sorted based on User's Feedback
Answer / v.selvakumar
mccb is a protect device,whenever short circuit fault
happens ,it will isolate healthy system from faulty system
due to heavy .changing the phase neutral in circuit not a
fault,it will work as normal circuit.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / pratheesh
What Mr.Rajan mantioned is not correct. Core Balance CT,
CBCT (Also called as Zero CT)is used for detecting the
earth fault current.
MCCB is a protective device by sensing the load current. By
interchanging the Phase and Neutral wires, there will not
be any difference in the load current.
So MCCB will trip on higher load current such as overload
or short circuit.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / rajan.l
Shunt Trip Coil is not connected with a core balanced CT
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / basayya hiremath
mccb is protectve divise over load and shotr ckt,dipinding
ka rating of the mccb supose 25 ka mcc using this mccb
withastading ofthe current up to 25ka .u whant when phase
and nutrul shotr downstrim side using the mcb this will
trip u what to nutrul protect or earth fualt u can use cbct
incomming side of the mccb with shunt coil in side the mccb
and defending opan idmt curv
| Is This Answer Correct ? | 0 Yes | 0 No |
If I have 3 essential main switch board and 3 incoming electricity ,but only 1 genset running is that possible.
Why the CT Secondary is rated as 5A generally?
There are two nos of 33Kv/11Kv 5MVA transformers conecting through HT cable from substation having metering at substation itself.One transformer used at a time another remains stand by.Further 11 nos of 11Kv/440V transformers are attached on it and each transformer is having its own Power factor correction panel.Now one 33/11Kv transformer at no load condition/Stand by condition is having power factor in leading side upto 0.21 and while when another tranformer at same situation have power factor in lagging 0.42. Now one thing is clear that transformer one is having 1.5 Km long 33kv cable due to that PF goes in leading side and another is having only 250 mtr length remains him lagging. Now i want to know that how i can maintain the Power factor at no load/ stand by position though both are behaving in seperate manner.
How to dimensioning SDCCH, LAPD and CS7 signaling on GSM?
What is Auto Mains Failure Panel & Auto Synchronizing Panel
WHY TRANSFORMERS ARE RATED IN 11KV 22KV 33KV Instead off 10kv 20kv 30kv
How star and delta connections inherently eliminate triplend harmonics?
How many types of circuit loads are there in a common electrical circuit?
What is the reasonable voltage between Neutral & Earth of an electrical system for good earthing?
what is the AC Plant and how can do the work with parts and picture tell us 150 Tr
where induction generator is used ?
ell me capacitor bank chossen formula.load in KW
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)