I have installed capacitor bank at secondary transformer.
cos phi is increase. but on load (far from transormer), it
still poor. Can anybody explain it??
Answers were Sorted based on User's Feedback
Answer / jinu
capacitor bank will improve the power factor towards the
supply side only. ie if you are measuring the power factor
before the capacitor bank it will show the improved power
factor. But the same time when you measure it after the
bank it will show you the load power factor not the
improved power factor.
| Is This Answer Correct ? | 19 Yes | 0 No |
Answer / heamkumar
Capacitor Bank is used to improve the Power Factor.
As you said, Pf will increase only in the incomer side.
Because you have connected the capacitor bank in the
secondary side near the incomer. So if you need to improve
the pf near load, you need to place the capacitor bank near
the load, but according to the load. So if you put the
capapcitor banks near the load side, power factor will
improve not only in the load side, but also in the incomer
side.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / joseph
Since the reactive power compensation (capacitor) is
provided on the LT side of the transformer, the
compensation will take place upstream from the point of
connection. Between the point of connection and the Load,
the reactive power still remains uncompensated. Hence, in
case the loads are not very small and vastly distributed in
the network, it is better to provide reactive compensation
at the load end itself. The only disadvantage is that
there should be arrangement to switch off these capacitors
when loads are not ON, otherwise, the capacitors themselves
would act as loads!
| Is This Answer Correct ? | 3 Yes | 1 No |
first a fall caluclate the reactive power. after that
according to reactive power caluclate requied capacitor to
be arrange then u will increase power factor.
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / niranajn
Because the capacitor abnk provides the ractive power
needed near a transformer but it cant provide the
kvar required by the line so the power factor is still
low
| Is This Answer Correct ? | 1 Yes | 4 No |
how wecalculate breaking capcity of acb mcb mccb .explain with example
HOW TO CALCULATE ELECTRICAL, MECHANICAL,& OVERALL EFICIENCY OF GAS ENGINE POWER PLANT
If a 3 phase transformer is a 500 kva using the formulae 500kva= 500000/433 x 1.732 = 666.71amps does this mean that each phase on the secondary side is 666.71
.php|
how DC motor operating in detail .pls any one guide me .iam not clear idea about that .thank u
Explain the construction of the conservator, operation and purpose, and draw the diagram of the conservator.
Will u plz give me simple diagram for tube light connection & also function of chock?
8 Answers Bhushan Power Steel, Dalmia Group, Jindal, Practical Viva Questions, TCS, Windmoller,
electromechanical relay type identification example : type=tjmh t-stants for j- m- h-
WHY WE DO NOT TAKE THE POWER FACTOR MORE NEARER TO UNITY IN AC GENERATOR?
What it the purpose of parallel phasing transfomers??
what is an oscillator?
what is blocking diode and what is the use of it in tne control circuit.Pls Explain it.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)