I have installed capacitor bank at secondary transformer.
cos phi is increase. but on load (far from transormer), it
still poor. Can anybody explain it??

Answers were Sorted based on User's Feedback



I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far fro..

Answer / jinu

capacitor bank will improve the power factor towards the
supply side only. ie if you are measuring the power factor
before the capacitor bank it will show the improved power
factor. But the same time when you measure it after the
bank it will show you the load power factor not the
improved power factor.

Is This Answer Correct ?    19 Yes 0 No

I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far fro..

Answer / heamkumar

Capacitor Bank is used to improve the Power Factor.
As you said, Pf will increase only in the incomer side.
Because you have connected the capacitor bank in the
secondary side near the incomer. So if you need to improve
the pf near load, you need to place the capacitor bank near
the load, but according to the load. So if you put the
capapcitor banks near the load side, power factor will
improve not only in the load side, but also in the incomer
side.

Is This Answer Correct ?    11 Yes 0 No

I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far fro..

Answer / joseph

Since the reactive power compensation (capacitor) is
provided on the LT side of the transformer, the
compensation will take place upstream from the point of
connection. Between the point of connection and the Load,
the reactive power still remains uncompensated. Hence, in
case the loads are not very small and vastly distributed in
the network, it is better to provide reactive compensation
at the load end itself. The only disadvantage is that
there should be arrangement to switch off these capacitors
when loads are not ON, otherwise, the capacitors themselves
would act as loads!

Is This Answer Correct ?    3 Yes 1 No

I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far fro..

Answer / vikramsena_reddy

first a fall caluclate the reactive power. after that
according to reactive power caluclate requied capacitor to
be arrange then u will increase power factor.

kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}

Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.

Is This Answer Correct ?    2 Yes 4 No

I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far fro..

Answer / niranajn

Because the capacitor abnk provides the ractive power
needed near a transformer but it cant provide the
kvar required by the line so the power factor is still
low

Is This Answer Correct ?    1 Yes 4 No

I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far fro..

Answer / mustafa

you have not adjusted the losses

Is This Answer Correct ?    1 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

What will happen if 230V DC motor connected to 230V AC Supply?

15 Answers   Ashok Leyland, BOC, JSW, ONGC, RRB, TRB,


Why CT secondary is grounded?

11 Answers   GE,


How many types of relay are present in a VCB and ACB, what are the tests we can conduct on both breakers and how to set the relays values

2 Answers   Hyundai, Sodexo,


what is the use of ballast in tube

2 Answers  


Define steady state error.

0 Answers  






why commutator is attached with only dc macine

8 Answers   ONGC,


how fluoresent lamp works??

2 Answers  


What is the formula to calculate distribution transformer De-rating on iron losses basis

0 Answers   IESCO,


if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?

3 Answers  


why the the phase transformer's nuetral has been grounded

2 Answers  


Is there any specialised book to refer about fault level calculation both in MV and LV side??

0 Answers  


how to calculate micom relay earth falt time and current sertting

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)