Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

I have installed capacitor bank at secondary transformer.
cos phi is increase. but on load (far from transormer), it
still poor. Can anybody explain it??

Answer Posted / heamkumar

Capacitor Bank is used to improve the Power Factor.
As you said, Pf will increase only in the incomer side.
Because you have connected the capacitor bank in the
secondary side near the incomer. So if you need to improve
the pf near load, you need to place the capacitor bank near
the load, but according to the load. So if you put the
capapcitor banks near the load side, power factor will
improve not only in the load side, but also in the incomer
side.

Is This Answer Correct ?    11 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the path of thunderlightening? once both a buffalo and a person were standing 5m apart but lightening hit and killed buffalo not person?

2848


1.ZEBRA conductor(large size) 2.KUNDHA conductor( small size ) 3.panther conductor(very small ) 4.lepard conductor (very very small)

2900


hr round

2108


what are problems caused by the pdu in rack server

1962


If two Transformers are connected in parallel having impedance of 50KA in both transformers will the impedance increase or decrease after connecting transformers in parallel?

2043


Can you please explain creepage distance in detail, for a 6.6kV cable head what must the distance be and how do you determine it?

2869


State Maximum Power Transfer theorem.

1240


Difference between on line capacitor and Station type capacitor

1999


For electrical designers what are the standard should know? i want learn about this standards. how to get information/reference. anybody help in this regards please.

2109


What is BusBar integrity test and how it is conducted?

2226


How is magnetic leakage reduced?

1146


Best way to measure the Soil resistance of rocky soil, three probe method and four probe method

1916


how you taken aotitude test

2470


can i connect wavetrap in 2 different phase in EHV line?

1819


What do you mean by a phase angel of instrument transformer?

1092