How to calculate earth flat size for 250 Kva DG and
transformer?
Answers were Sorted based on User's Feedback
Answer / ashish
Any DG Require Four earthing strip Two For Neutral Earthing
& Two For Body Earthing.
Incase of 250 KVA DG 30X6 mm GI Earthing Strip is Suitable.
| Is This Answer Correct ? | 50 Yes | 24 No |
Answer / ajaydoss
Thanks for reply. I need the calculation (formula) .
| Is This Answer Correct ? | 29 Yes | 15 No |
Answer / ramesh p n
Voltage is the potential difference between two Conductors,
for Single Phase and the fro three phase system it is the
potential Difference between three phases and the neutral
for Example in india WE have 240 Volts A C Voltage for
single phase and 415 V for 3 Phase,
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
| Is This Answer Correct ? | 17 Yes | 8 No |
THE RATED CURRENT OUTPUT WILLBE 434AMP AND THE EARTH
CONTINUITY CONDUCTOR SHOULD BE HALF OF THE LARGEST CURRENT
CARRYING CONDUCTOR.
IF THERE IS CU CONDUCTOR OF SIZE 400SQ. MM IS USED THEN
EARTH CONDUCTOR SHOULD BE 200 SQ. MM OF DIMENSION 40X6 CU
STRIP CAN WORK EFFECTIVELY.
| Is This Answer Correct ? | 14 Yes | 12 No |
Answer / anupam mahesh
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / rsbangra
what is the voltage level ?
kva =1.732*v*i
i=kva/1.732*v
we get current value then find out current carring bus size
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / samson
Neutral will come in to picture whenever u start ur DG (
and not paralleing with a Grid as it will create a
circulating current), so worst thing that can happen is L.G
fault on a phase of generator or inside the winding , so
max current that can go is dg rating/ phase volatge ( use
formula above) so ur neutral should be capable of that
much curent ,( neglecting any contact resistance in ideal
case)
the switching of neutral is done through contactor.
use this to size strip
the I = K* A/ sqrt of time ( some of IS standered give u k
for bare conductor) Dg manufacturer will size support for
S.C forces
get k for alumi. or copper u can size to next standered
sizes available 20 x 6, 40 x5 n all
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / dg
Current should be 348Amp. As DG of 250KVA not 250Kw. So PF wont be used to calulate current.
| Is This Answer Correct ? | 4 Yes | 8 No |
send me all basic electrical question and answers
I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current 36 A,but wenn i put load after 2 hours the current increase more than 156 A. Can anybode tell me waht is the Problem?
Can someone tell me how to calculate the size of a power cable? What are the factors involved in cable sizing?
what will happen if i connect or change line with phase terminal
We all have seen transmission and Distribution lines In transmission lines the voltage is high and current is low(to reduce I^2r loss) and in distribution lines voltage is low but current is high however the size of transmission wires is bigger than that of distribution wires even though the amount of current carried by the distribution lines is more than that of transmission lines why?
what is the power factor
13 Answers Heidelberge Cement,
Hello sir i m student of gtu .what is idp.
Why should we use Star-Delta connection in step down power transformers?
PLEASE SEND ME NTPC RELATED INFORMATION LIKE WHICH TOPICS HAV MORE SCOPE,BOOKS TO READ,CUT OFF...PLEASE.mail at thiru.1203@gmail.com
In our plant we have installed new MCC with ELR and CBCT which is detecting some leakage current in the system but it leading to some confusion when to check that in which feeder which is drawing current we put off the whole panel itself but still CBCT detecting some leakage current so can anybody ans me , where i am going wrong or how to detect whether its actual leakage or CBCT malfunctioning.
Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.
what is ballast
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)