Answer / ashish
Any DG Require Four earthing strip Two For Neutral Earthing
& Two For Body Earthing.
Incase of 250 KVA DG 30X6 mm GI Earthing Strip is Suitable.
| Is This Answer Correct ? | 50 Yes | 24 No |
Answer / ajaydoss
Thanks for reply. I need the calculation (formula) .
| Is This Answer Correct ? | 29 Yes | 15 No |
Answer / ramesh p n
Voltage is the potential difference between two Conductors,
for Single Phase and the fro three phase system it is the
potential Difference between three phases and the neutral
for Example in india WE have 240 Volts A C Voltage for
single phase and 415 V for 3 Phase,
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
| Is This Answer Correct ? | 17 Yes | 8 No |
THE RATED CURRENT OUTPUT WILLBE 434AMP AND THE EARTH
CONTINUITY CONDUCTOR SHOULD BE HALF OF THE LARGEST CURRENT
CARRYING CONDUCTOR.
IF THERE IS CU CONDUCTOR OF SIZE 400SQ. MM IS USED THEN
EARTH CONDUCTOR SHOULD BE 200 SQ. MM OF DIMENSION 40X6 CU
STRIP CAN WORK EFFECTIVELY.
| Is This Answer Correct ? | 14 Yes | 12 No |
Answer / anupam mahesh
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / rsbangra
what is the voltage level ?
kva =1.732*v*i
i=kva/1.732*v
we get current value then find out current carring bus size
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / samson
Neutral will come in to picture whenever u start ur DG (
and not paralleing with a Grid as it will create a
circulating current), so worst thing that can happen is L.G
fault on a phase of generator or inside the winding , so
max current that can go is dg rating/ phase volatge ( use
formula above) so ur neutral should be capable of that
much curent ,( neglecting any contact resistance in ideal
case)
the switching of neutral is done through contactor.
use this to size strip
the I = K* A/ sqrt of time ( some of IS standered give u k
for bare conductor) Dg manufacturer will size support for
S.C forces
get k for alumi. or copper u can size to next standered
sizes available 20 x 6, 40 x5 n all
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / dg
Current should be 348Amp. As DG of 250KVA not 250Kw. So PF wont be used to calulate current.
| Is This Answer Correct ? | 4 Yes | 8 No |
What is sequence network? Discuss all three types of sequence network.
why breaker closing coil gets burnt if supply is continously provided to it.
how is motorized megger operate?
if we want ot select cable size with reference to load current it take than what is the formula and it is same for aluminium or copper?
There is no such thing as a Generator. All power generating devices are Alternator since both generate alternating current since this is the only way electrical power can be generated. In "generators" the alternating current is converted into DC inside the housing of the "generator" in order to give out DC Do you agree? If not please educate me. How else is DC generated if not like above?
State ohm’s law?
what id a dry type transformers and its function ?
Is Softbitonline HT Transformer Design Software is AutoCAD compatible?
Why star point of star connected motor is not grounded? Why alternator is operated at lagging power factor?
if power factor comes in leading & showing -0.95. Is there any effect on electrical system? if yes, then please tell me what would be the effects. & how long we keep power factor in leading. Keeping power factor in leading shows more KW & less KVA is it correct or not.
why there using acb enclosure in big buildings
In case of motor Power Factor Generally We Apply A Capacitor But How Can We Know That A Motor is Running On Very low Power Factor And What Rating Of Capacitor We Have To Place And Tell Me Conversion Of Micro Farad to KVAR>
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)