How to calculate earth flat size for 250 Kva DG and
transformer?
Answers were Sorted based on User's Feedback
Answer / ashish
Any DG Require Four earthing strip Two For Neutral Earthing
& Two For Body Earthing.
Incase of 250 KVA DG 30X6 mm GI Earthing Strip is Suitable.
Is This Answer Correct ? | 50 Yes | 24 No |
Answer / ajaydoss
Thanks for reply. I need the calculation (formula) .
Is This Answer Correct ? | 29 Yes | 15 No |
Answer / ramesh p n
Voltage is the potential difference between two Conductors,
for Single Phase and the fro three phase system it is the
potential Difference between three phases and the neutral
for Example in india WE have 240 Volts A C Voltage for
single phase and 415 V for 3 Phase,
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
Is This Answer Correct ? | 17 Yes | 8 No |
THE RATED CURRENT OUTPUT WILLBE 434AMP AND THE EARTH
CONTINUITY CONDUCTOR SHOULD BE HALF OF THE LARGEST CURRENT
CARRYING CONDUCTOR.
IF THERE IS CU CONDUCTOR OF SIZE 400SQ. MM IS USED THEN
EARTH CONDUCTOR SHOULD BE 200 SQ. MM OF DIMENSION 40X6 CU
STRIP CAN WORK EFFECTIVELY.
Is This Answer Correct ? | 14 Yes | 12 No |
Answer / anupam mahesh
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / rsbangra
what is the voltage level ?
kva =1.732*v*i
i=kva/1.732*v
we get current value then find out current carring bus size
Is This Answer Correct ? | 8 Yes | 8 No |
Answer / samson
Neutral will come in to picture whenever u start ur DG (
and not paralleing with a Grid as it will create a
circulating current), so worst thing that can happen is L.G
fault on a phase of generator or inside the winding , so
max current that can go is dg rating/ phase volatge ( use
formula above) so ur neutral should be capable of that
much curent ,( neglecting any contact resistance in ideal
case)
the switching of neutral is done through contactor.
use this to size strip
the I = K* A/ sqrt of time ( some of IS standered give u k
for bare conductor) Dg manufacturer will size support for
S.C forces
get k for alumi. or copper u can size to next standered
sizes available 20 x 6, 40 x5 n all
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / dg
Current should be 348Amp. As DG of 250KVA not 250Kw. So PF wont be used to calulate current.
Is This Answer Correct ? | 4 Yes | 8 No |
I've descovered that when the earth wire in a domestic electrical installation is not connected back to the board (ground) a voltage of between 9-24v is is found to be present in the earth wire. When connected at the board there is no voltage - is this normal and why does it happen?
How I can Compare 120v/60Hz versus 220v/50Hz ? Please tell me both advantage and disadvantage ......
3phase motor 400v (induction) A.C 4kw company design 1400rpm but our requirement 2000rpm possible? attached any instrument. reply fast! contact 03343262442
how to syncronize two dg sets
basic princple of induction and synchronous motor
When the relative speed between the magnetic fields of stator and rotor does is zero under steady state operation?
It is desired to flood light the front of a building 42 meters wide and 16 meters hig.Projectors of 30 degree beam spread and 1000 watt lamps giving 20 lumen/watt are availabl.If the desired level of illumination is 75 lumen/m and show a suitable scheme.Assume the cofficient of utilization, deprecitation factor and waste light factor are 0.4, 13 and 1.2 respectively.
3ph motor running with unequal kw and different pf what are the reasons
what is the Transformer Protection & Type ??
explain all the classes with example
How does and Earth Fault Relay operates in DG set control panel?
1 Answers Cummins, University,
when two gen set runing in parallel but thay have diffrent pole pitch, then what will be happan