Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

Two electronic energy meters are connected to seperate
phase wires, but connected to a looped neutral. Are these
going to function correctly?

Answer Posted / dilip kumar

ofcourse both will work satisfactorily ,but if the
connection is used for measurement of 3-phase power then it
will nither give the correct power nor the correct phase

Is This Answer Correct ?    4 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

plz send me the placement interview question and answers of whizchip(technical and apttitude)..i have an interview in next.

4956


TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2

2350


full form of flry b

4111


What is the meaning of HT Trivector Meter ?

2384


How to calculate fault level of 11 KV system

2020


3ph motor running with unequal kw and different pf what are the reasons

1767


What is the formula to calculate the rating of a three phase air circuit breaker

2270


EXPLAIN THE TRANSFORMER MAINTENANCE?

2201


why transformer tank is in rectangular shape what happen when it is in step shape

1390


What is the difference between AC and DC injection methods for rotor earth fault protection

2148


Define filter?

1059


A generating system will have a total capacity of 300 MW. Find the probable forced outage when the capacity is supplied by two 150 MW units. The operating probability of all units is P=0.98 and forced outage probability rate Q =0.02 .

2578


What is the feedback in the control system?

1031


In convertor can we use rectifier thyristor in place of invertor thyristor with explain.

1755


How much ph is maintained of water resistance starter for slipring induction motor ?

2350