HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM

Answers were Sorted based on User's Feedback



HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / kalirajan.n

TAKE A LOOK IN THE FORMULA BELOW....

VD= 2*K*I*L/ CSA

WHERE:

VD= VOLTAGE DROP
I= CURRENT
L= DISTANCE OF THE LOAD FROM THE OUTLET (IN FT)
K= 12 FOR COPPER AND 19 ALUMINUM (FOR MAXIMUM TEMP OF 75 DC)
CSA= CONDUCTOR CROSS SECTIONAL AREA IN CIRCULAR MILS.

Is This Answer Correct ?    55 Yes 20 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / himadri nayak

Copper Wire
Single Phase/Circuit
Voltage 240
Power(W) 1000
Power Factor 0.8
Resistivity(at 15 c) 1.72E-08
Tempertature 35 C
Resistivity 3.096E-08(for copper)
Length(m) 300(phase+neutral)
Cross section(m2) 0.000006
Resistance 1.55
Load 5.21
Voltage drop 8.06
Percentage 3.36(Do not go above 3 %)
Actual voltage 236.64
Actual Current 5.28

This is a sample of how to calculate wire size for single phase copper wire. If you want contact me for the excel sheet for copper/Al, 3phase/1 phase calculation.

@ himadrinayak@yahoo.co.in

Is This Answer Correct ?    31 Yes 5 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / dilawar husain

yes,these factors are important for cable sizes.

Is This Answer Correct ?    25 Yes 7 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / venkat iyer

Factors that to be considered are;

1. ambient temperature
2. permitted temperature rise
3. factors applicable due to method of cable laying
4. factors applicable for group running of cables
5. spacing between cables
6. permitted voltage drop say 2.5%

Is This Answer Correct ?    24 Yes 7 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / jignesh panwala

IT IS BAISICALLY DPEND UPON THE LOAD.
SUPPOSE 53 A LOAD.
53/1.5= 35 HP
35*0.746=26 KW
26000/690=38 SqMM
THIS CALCULATION IS FOR AL CABLE

Is This Answer Correct ?    34 Yes 20 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / sivakumar

As per answer no 5, how you take 1.5 and 690 values for
calculation? is there any reference about that value

Is This Answer Correct ?    22 Yes 8 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / rajnikant

Dear himadri,
i need more details for the calculation of copper and
aluminium sizes of cable and current capacity.

Is This Answer Correct ?    11 Yes 0 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / bubbly

Actually all brothers we want to know calculation of cable
not VD so please any one have calculation of cable on load
& distance attach here

Is This Answer Correct ?    9 Yes 0 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / kalirajan.n

***SUPPOSE WE USE COPPER CONDUCTOR AND WE ALLOW A MAXIMUM OF
5V MAX. VOLTAGE DROP:

5= 2*12*15*230/CSA

CSA= 82800/5

CSA= 16560 CM

FROM COMMERCIAL REFERRENCES:

15560 CM IS CLOSEST TO 16510 CM WHICH IS #8 COPPER OR 8 SQMM
WIRE.

NOTE:

1. IN THIS CASE A MAXIMUM OF 5 VOLTS WAS CONSIDERED IN THE
CALCULATION.

2. THIS CALCULATION IS NOT VALID FOR LARGE MOTORS. BECAUSE
MOTORS DRAWS A MAXIMUM OF 7OO% TIMES ITS FULL LOAD TORQUE
DEPENDING ON THE MOTOR CONTROL STARTING METHODS USED BY THE
DESIGNING ENGINEER.

Is This Answer Correct ?    14 Yes 8 No

HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM..

Answer / rohit

Dear himadri nayak could you please tell me the formula to
calculate V.D...and exact formula for calculation of cable
size..but not taking any factor as assuming,,,and if u r
assuming then hw ur assuming????dear you can mail it to me
if you dont mind..
Thanks & regards
ROHIT

waiting for your reply ASAP....

Is This Answer Correct ?    5 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

whether fibre optic cable in high voltage earth conductor is used for protection circuits

0 Answers  


what will happen if any motor runs long time with star connection in400vA.C. system

5 Answers  


difference between isolator and circuit breaker?????

7 Answers   Enercon,


What is the megger value for ht

16 Answers   Electrical,


I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?

0 Answers  






What are the factors to be considered during the Synchronization?

3 Answers  


1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason

16 Answers   Ecil, Engineers India, MahaDiscom,


How to calculate Busbar Thickness for Different type of HT/LT panels

1 Answers  


how to find out 3 phase complex power in per unit in unbalanced system?

0 Answers  


what will be d.g. capacity to cater together for 14hp A.C. load & 3kw lighting load

0 Answers  


Define newton's law of viscosity.

0 Answers   Godrej,


how much the voltage & resistance should be ,between earth & neutral points.?& why?

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)