in our transmisison sub station why we step down firstly
132kv\33kv then 33kv to 11kv. can we direct step down 132kv
to 11kv.
Answers were Sorted based on User's Feedback
It is only for easy transmission and distribution. 11 kV
is normally used for town distribution. 33kV is used for
transmission to farther areas where the voltage is stepped
down by 33/11 kV sub stations. Normally in 132 incoming sub
stations you will have both 33 kv and 11 kV outgoings
depending upon the location of the 132/33/11 kV sub station.
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / rakesh verma
1)yes you can directly stapdown 132 kv to 11 kv but in
general cases our transimision outgoing feeder may be
66kv,33kv or 11kv thats why we stap down 132/33/11kv ,if 33
kv not required then we can direct stapdown 132kv to 11kv
2)You can certenly step down the voltage from 132 KV to 11
kv , however in Distribution Substation diffrent level of
voltage comes across so as in your case your substation
should have a diffrent outgoin feeders of 33 kv so your
distribution is 132KV / 33 KV / 11 KV...
3)It is only for easy transmission and distribution. 11 kV
is normally used for town distribution. 33kV is used for
transmission to farther areas where the voltage is stepped
down by 33/11 kV sub stations. Normally in 132 incoming sub
stations you will have both 33 kv and 11 kV outgoings
depending upon the location of the 132/33/11 kV sub station.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / manish
Yes you can directly stapdown 132 kv to 11 kv but in
general cases our transimision outgoing feeder may be
66kv,33kv or 11kv thats why we stap down 132/33/11kv ,if 33
kv not required then we can direct stapdown 132kv to 11kv
| Is This Answer Correct ? | 1 Yes | 2 No |
Dear Mottaleb
You can certenly step down the voltage from 132 KV to 11
kv , however in Distribution Substation diffrent level of
voltage comes across so as in your case your substation
should have a diffrent outgoin feeders of 33 kv so your
distribution is 132KV / 33 KV / 11 KV...
| Is This Answer Correct ? | 2 Yes | 4 No |
Is MV canble armour can be earthed at both ends?
What is sink and source?
kVA rating of open delta connected transformer is _____% kVA rating of delta/delta connection A 50 B 70.7 C 57.7 D 75.7
how can you size an automatic voltage regulator?
what is meant by trip circuit supervision & directional or non directional over current ?
If a air condition consume 2.50 to 3.00 amp then how much it will consume in watts if it is running 10 hours out of 24 hours????
advantages & Disadvantages of Solar power system?
WHAT IS THE DIFFERENE IN ACTION OF MCB,MCCB,RCCB
what is brushless generator.How does work it..??
what are the C&D CHECK OF DG set
Why underground cables are used to connect transformers?In addition how are they again connected to lines after step up or step down?
after how many spot we must chang secondry cable in portable spot welding gun?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)