Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why transformer rating in kva ?

Answers were Sorted based on User's Feedback



why transformer rating in kva ?..

Answer / panda n.n

Transformer has two type of loss.1-Iron Loss ,2-Copper Loss.
Iron loss depend upon Voltage where as copper loss depend
upon Current. ther is no significant role of power factor
on these losses.So transformer are rated on KVA or MVA.

Is This Answer Correct ?    65 Yes 5 No

why transformer rating in kva ?..

Answer / pankaj

TRANSFORMER LOSSESS ARE INDEPANDANT OF POWER FACTOR BECAUSE
COPPER LOSSES DEPENDS ON CURRENT AND IRON LOSSESS DEPENDS
ON VOLATGE. HENCE, RATED IN KVA

Is This Answer Correct ?    18 Yes 2 No

why transformer rating in kva ?..

Answer / srinu

in tf core lossdepends on voltage rating and cu loss
depepends on current ,as the rating of any machine depends
on it's heating that is losses. so in tf heating is
proportional to product of v and i.so tf rating is in terms
of kva rather than kw.
and one more reason is as the load on tf is not constant,we
dont know the exact power factor value.that is also one of
the reason to express tf rating in kva.

Is This Answer Correct ?    5 Yes 1 No

why transformer rating in kva ?..

Answer / pritesh

simple, the load which is joint with the transformer is not
known so that we dont know the actual power factor because
of reasion the rating of the transformer is in the kva not
in kw.

Is This Answer Correct ?    12 Yes 10 No

why transformer rating in kva ?..

Answer / rcv

It is because of load power factor,Transformer is always
designed on unity power factor. It has only 2 type of
losses Iron loss due to voltage, I2R loss and Stray loss
due to load and there is no involment of powerfactor. Thats
why transformer is rating in KVA.

Is This Answer Correct ?    1 Yes 0 No

why transformer rating in kva ?..

Answer / aditya shirbavikar

The power factor of transformer is unknown and is derived according to the load connected. Therefore the rating of transformer is in KVA

Is This Answer Correct ?    1 Yes 0 No

why transformer rating in kva ?..

Answer / syed vikhar ahmad

power factor is not constant it varies in different load
thats why manufaturer can not keep the rating in kw.suppose
the transformer rating is 500 kva we can put 500 kw load at
unity power factor but at .8 power factor we can put only
400 kw load as per formula kw= kva* pf

Is This Answer Correct ?    0 Yes 0 No

why transformer rating in kva ?..

Answer / saida shaik

KVA is the unit for apparent power
Apparent power consists of Active and Reactive power. Active power is transmits energy from the source to the user. Reactive power is represents a usless oscillation of energy from the source to the user and back again. Reactive power occurs when on account of some inertia in the system there is a phase shift between voltage and current. This means that the current dose not change polarity synchronous with the volage but the heat generated in a winding as well as the eddy current losses generated in a t/f core depend on the current only ,regardless of whether it aligns with the voltage or not. Therefore the heat is always propotional to the square of the current amplitude irrespective ofphase angle so a t/f has to be rated by apparent power.(it means KVA instead of KW)

Is This Answer Correct ?    0 Yes 0 No

why transformer rating in kva ?..

Answer / a.alexander

do n't know the connecting load .for inductive load ,
capacitive load and Reactive load. transformer is copper
loss dependable for I and core loss dependable for v .told
Kva.

Is This Answer Correct ?    9 Yes 12 No

why transformer rating in kva ?..

Answer / joseph

since it has no load losses, transformer rating in KVa

Is This Answer Correct ?    1 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

Define magnetic centre in a motor?

1 Answers  


We have 250 KW x 2 motors, which are load from 25% to 100% varying load in every minute , so how can we compansate the power factor. pl give your opinions on the above subject.

0 Answers  


Why transformer neutral earthing? What is advantages?

6 Answers  


how much insulation resistance 11kv & 33kv under ground cable between earth to phase & phase to phase.

4 Answers   Siemens,


What is the minimum value required for Neutral to Earth in UPS Panels

3 Answers  


why we use lamination or layer by layer cor used?

4 Answers  


What is the reasonable voltage between Neutral & Earth of an electrical system for good earthing?

6 Answers   HAL,


why using touble tube lamp use in factory?

3 Answers   ONGC,


how to calculate Transformer loss?

1 Answers  


Auto transformer starter gives the same effect as star/delta strater if its turn ratio = A 0.5 B 0.67 C o.66 D 0.577

1 Answers  


what is the role of transistor in Circuit?

0 Answers  


why power of fm is weaker than am?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)