how to calculate the KVAr for an motor for improving the PF
Answers were Sorted based on User's Feedback
Answer / guest
Example:Calculation of the kVAR rating for 1750kW Motor
Motor Data:
Rating of Motor: 1750kW
System voltage: 6.6kV
Power factor of the motor when running at 75% of full
load : 0.84
(Power factor of the motor is considered at 75% of full
load, assuming that the motor will be loaded at an average
of 75%)
Target Power factor : 0.95 lag ( To improve the power
factor from 0.84 to 0.95, after adding the capacitor bank
in the motor circuit)
Required kVAR of the Capacitor Bank to
achieve the target power factor.
KVAr = KW ((TanQ1- TanQ2)
where
Q1= Cosinsverse(P.F1)Initial Power Factor Angle
Q2= Cosinsverse(P.F2)Target Power Factor Angle
So, required kVAR
=0.75*1750*(tan (cos-1 (0.84)) - tan (cos-1 (0.95)))
= 416kVAR
Is This Answer Correct ? | 65 Yes | 10 No |
practicalLY what is impedence ...?
when qty of cable being purchased is not sufficient according to the standard,what should the inspector do to ensure its quality according to the standard?
As per the Anchor capstan motor specification, full load current is 200A. starting current is 1750 A and acceleration time is less than 8 seconds. Please guide for selection of cable size.
what is difference between 9kv 5ka surge arrester and 9kv 10ka surge arrester.
what are the functions of current transducer and voltage transducer?
Which type of moter is used in trains, what is the ratting of supply used explain Working principal?
why in transformers voltage given is in the multiple of 11
what is a pf factor in generator.
PLC Based Process Automoation Panels?
where reactive power is used
two bulbs of 100w and 40w respectively connected in paralel across a 230v supply.which bulb will glow bright and why?
What are the causes for the failures of sandwich type (Al) busducts?