how to calculate the KVAr for an motor for improving the PF
Answers were Sorted based on User's Feedback
Answer / guest
Example:Calculation of the kVAR rating for 1750kW Motor
Motor Data:
Rating of Motor: 1750kW
System voltage: 6.6kV
Power factor of the motor when running at 75% of full
load : 0.84
(Power factor of the motor is considered at 75% of full
load, assuming that the motor will be loaded at an average
of 75%)
Target Power factor : 0.95 lag ( To improve the power
factor from 0.84 to 0.95, after adding the capacitor bank
in the motor circuit)
Required kVAR of the Capacitor Bank to
achieve the target power factor.
KVAr = KW ((TanQ1- TanQ2)
where
Q1= Cosinsverse(P.F1)Initial Power Factor Angle
Q2= Cosinsverse(P.F2)Target Power Factor Angle
So, required kVAR
=0.75*1750*(tan (cos-1 (0.84)) - tan (cos-1 (0.95)))
= 416kVAR
| Is This Answer Correct ? | 65 Yes | 10 No |
Explain what is electric traction?
why generator one end side star neutral point given? if this point not given what happen?
if its possible for step up or step down DC volage directly ? possible means how we can do it ?
Explain the Term in CT Name Plate – Class: 5P10
In a d.c circuit, if current and resistance are known, power (P=I*I*R) can be determined. This relationship also applied to an a.c circuit. Comment the reason for this.
every motors written in name plate IP 55 what is this?
what is formula of dc current and resistance.
After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.
How can we explain that what is the power factor?
Why stand-by earth fault relay and restricted earth fault relays are connected between neutral and ground in transformer?
we have 400kv/6.6kv transformer ,it has total 9 taps on HV side with normal tap on tap no 5.when we took the ratio test we observed that ratio was decreasing from tap 1 to tap 5 and was found increasing from tap 5 to tap 9.What is the reason?if anyone have related document then please send me on the email id ankushbahale@gmail.com......plz plz
why we don't use earthing as neutral?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)