how to calculate the KVAr for an motor for improving the PF
Answers were Sorted based on User's Feedback
Answer / guest
Example:Calculation of the kVAR rating for 1750kW Motor
Motor Data:
Rating of Motor: 1750kW
System voltage: 6.6kV
Power factor of the motor when running at 75% of full
load : 0.84
(Power factor of the motor is considered at 75% of full
load, assuming that the motor will be loaded at an average
of 75%)
Target Power factor : 0.95 lag ( To improve the power
factor from 0.84 to 0.95, after adding the capacitor bank
in the motor circuit)
Required kVAR of the Capacitor Bank to
achieve the target power factor.
KVAr = KW ((TanQ1- TanQ2)
where
Q1= Cosinsverse(P.F1)Initial Power Factor Angle
Q2= Cosinsverse(P.F2)Target Power Factor Angle
So, required kVAR
=0.75*1750*(tan (cos-1 (0.84)) - tan (cos-1 (0.95)))
= 416kVAR
| Is This Answer Correct ? | 65 Yes | 10 No |
what are the units of cable insulation?
How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)to improve the power factor from 0.8 to 0.9?
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
Am using an electronic digital display to see the RPM of ABB ACS 550 drive, which is showing negative value when the motor & drive in stop mode but it is showing correct value during the run mode. can anyone help me out??
2 Answers Bala Power Solutions,
what is the use of buchzloys relay?
difference between turns ratio and transformation ratio?
Why is tan-delta test and capacitor measurement done on alternator?
Residual voltage & residual current used in which protection?
5 Answers Qatar Gas, Reliance, Transformers and Electricals,
In Induction machines which type of emf is induced ( statically or dynamically)?
why and how fault current flows through ground?
During the testing of Electrical Equipment the test cables should not touch the equipments. For that testing engineers use to cotton rope to hang the cable from measuring Equipment to testing equipment terminal. Please explain the technical reason for this practice.
what is meant by magnetic flow meter ? explain its working principle ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)