Answer / shan
we are to calibrate at the pressure switch. Pressure switch
is the pressure reciever.we have to set the pressure switch
at 2Kg/cm2. If pressure reaches 2Kg/cm2,it will alarm.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / mithilesh kumar
1st pr. switch is combination of NO,NC,COMMON.OK.
for setting alarm at 2kg/cm2.
it calibrate with DEAD WEIGHT TESTER at 2kg/cm2.during
calibration NC becomes NO and NO become NC.it check with
multimeter in continuity mode.ok.
if it's done then your calibration is ok.
then you can use as per requirement.
any comment.
most welcome
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / welcome4ujd
if range is 0 to 8 kg/cm2, an d alarm needed is 2 kg/cm2.
that is 25 percent of range, set the alarm at 6 psi of a 3
to 15 psi out put.
and if it is a flow transmitter of some range,say 0 to
1000 mmwc and alarm at 250 mm
then 25 % of flow in transmitter will give square root 25
devided by 10 tht is 50 percent in the control room , so
you have to set 50percent in the receiver switch that is 9
psi for a 3 to 15 psi out put.for basic flow transmitter
to find out square rooting from field to ccr
just square root the input percentage and devide by 10
to find the field input from control room signal
devide the ccr signal percentage by 10 and square it.
| Is This Answer Correct ? | 2 Yes | 7 No |
what is the principal of coriolis mass flowmeter
what is preventive maintenance , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
what is formula for calculating flow if i have pressure and pipe diameter?
What is the working principal of Mass flow transmitter?
why cant we use mV instead of mA?
12 Answers ABB, Power Grid, Qatar Gas, USW, Visa Steel,
What is frequency factor in massflow meter? When using frequency output?
What is the meaning of wet leg
WHAT IS DIFFERANCE BETWEEN INSTRUMENT AND EQUIPMENT
any body pl suggest me the best type of transmitter for level monitoring of a distillation still which consists of highly corrosive and inflammable liquid.closed vessel height=5000mm especially in petrochemical industries
What is the Difference between CNC and PLC
what is plc communication?
WHAT IS ANNUBAR?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)