Range 8 Kg/cm2, alarm to be set at 2Kg/cm2, at wat pressure
reciever switch to be calibrated? justify the ans?
Answers were Sorted based on User's Feedback
Answer / shan
we are to calibrate at the pressure switch. Pressure switch
is the pressure reciever.we have to set the pressure switch
at 2Kg/cm2. If pressure reaches 2Kg/cm2,it will alarm.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / mithilesh kumar
1st pr. switch is combination of NO,NC,COMMON.OK.
for setting alarm at 2kg/cm2.
it calibrate with DEAD WEIGHT TESTER at 2kg/cm2.during
calibration NC becomes NO and NO become NC.it check with
multimeter in continuity mode.ok.
if it's done then your calibration is ok.
then you can use as per requirement.
any comment.
most welcome
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / welcome4ujd
if range is 0 to 8 kg/cm2, an d alarm needed is 2 kg/cm2.
that is 25 percent of range, set the alarm at 6 psi of a 3
to 15 psi out put.
and if it is a flow transmitter of some range,say 0 to
1000 mmwc and alarm at 250 mm
then 25 % of flow in transmitter will give square root 25
devided by 10 tht is 50 percent in the control room , so
you have to set 50percent in the receiver switch that is 9
psi for a 3 to 15 psi out put.for basic flow transmitter
to find out square rooting from field to ccr
just square root the input percentage and devide by 10
to find the field input from control room signal
devide the ccr signal percentage by 10 and square it.
| Is This Answer Correct ? | 2 Yes | 7 No |
What is difference between ESD and PLC please Explain me clearly.
why we use only 4 to 20ma other than 0 to 16 ma
How do bending tubing provide better measurement than using tubing fittings such as elbows?
Basics Instrumentation Question
1 Answers Advantek Fuel Systems,
how to calculate density?
Intools training
how to check electrical health of vibration probe?
how to convert % to ma
1 Answers Flour Tech Engineers (P) Ltd, Techint,
I have installed a RTD whose length is 2250mm(RTD stem length), but it's upper 200 -250mm is out of the reactor, and this upper 200mm stem is surrounded by atmospheric temp. And the lower portion i.e. 2000mm is in contact with the measuring fluid, then does the final measuring temp. Gonna change as the upper 200mm RTD stem is out of reactor?
1 Answers Process Control Technologies,
types of cable..? Use of every types of cable..?
What is 3 selection available when configure the burnout protection for controller
0 Answers EI Electrotechnical Institute,
What is a snubber circuit?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)