Answer / sks
well, increasing D action for a controller can make a
controller random in error elimination because even for a
step change D generates a spike( means tries to compensate
for change very quickly). if its increased to its limits, D
action will overtake the process value change and this will
cause further offsets that I action wouldn't be able to
compensate due to its slow response against such a rapid error.
result is a quick overvalued offset !
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / david
In PID
P is Propositional means it will adjust the output propositional to the error. For example a Tacho connected to a motor, to control it's Torque and RPM at a constant level.
I is Integral means calculating the area, according to the area of the error the output is adjusted. For example, the difference between positive cycle area and negative cycle area.
D is differentiation means calculating the angle difference and driving output for example
In a 3-phase system, If the load on R-phase is more than other two phases, phase angle
difference will occur so it will calculate the angle and drive output For example Auto Power factor adjuster.
| Is This Answer Correct ? | 0 Yes | 0 No |
how to use one 4-20mA signal for two indicater or controller & give necessary precaution.
Y to use 4 to 20ma instead of 0-10v
why we are using orfice plate? then difference between orfice 7 nozzle plate?
1 Answers Flour Tech Engineers (P) Ltd,
How signals can be taken through modbus?
HOW TO CALCULATE WAKE FREQUENCY FOR THERMOWELL???WITH OUT SOFTWARE..
field bus transmitter calibration procedure tell me
what is the difference between(Flame proof/Explosion proof)& Fire proof instruments.Both are same or different & if different in which way because the transmitter which have approved ATEX flame proof enclouser but it use PTPE O ring & PTFE Head Gasket,so its (fire safe/fire proof)????????
Dear All can any one told me that VFD Make ABB Model ACS800-01 used for dual Source like 1.DC Source applied at terminal UDC+,UDC- 2. 3 phase 400AC,50Hz
What is cut off relay? And why use in PLC and DCS?
How can one improve linearity of an RTD based temperature measurement system?
Q- Which of the following is Close loop system - a-)respiratory System b-)traffic light system c-)washing machine d-)Room heater my option is A, what is our take on option B & C
For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)