What type of protective system we uses in L.V. distribution
panels?
Answers were Sorted based on User's Feedback
Answer / satya dev
1-Over current & earth fault relay for feedar Protection.
2-reverse power relay for Alternators ( if diffrent
sourcees are used- eg. transformer supply & DG supply)
3-Inverse/differetial relay for Busbar protection.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / vel
over current and earth fault relays (2OL+1EL method)are
used for lv .
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jagadisha.n bmsit
Different protection systems which is used in LV panels are:
1. Short circuit protection :- It is done by choosing set
point in sc protection relay which is present inside the CB's.
2. Thermal protection for Busbars/ cables:- Bec extreme
thermal point cause flash over
3. Over current protection
4.Protection provided by proper shielding & interlocks such
that operator & maintenance people can not accesses live parts
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sachin
1.over current reley
2.earth fault reley
3.fase failure relay
3.fuse moniterning relay.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / nagesh
current protection
1)over current
2)short ckt current
3)Instantanious current
Earth fault relay,
Negative phase sequence
Phase failure
If require
High temprature
High vibration
Safety (door switches)
MD over shoot(MD monitoring)
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the relationship between current and frequency in AC circuit?
How to get Electrical Supervisory Licence in chennai Tamil Nadu from TNEB. I am BE EEE graduate.
IDMT relay are mostly used for protection against..??? 1)Earth Fault 2)Inter turn fault 3)Overloading 4)None of the above
in 50 mw generator if field is open in full load running condition what happen and for protection which relay used?
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
how to select power and control contactor .
IN bateery size of positive is biger than negative .why?
whit is 33kv power 300*300 cable full current with formula
3. What is Impedance Voltage in Transformer?
16 Answers KESC, L&T, Torrent Power,
what is the difference between ACTIVE POWER and REACTIVE POWER.I WANT CLEAR ANSEWER.
Why should be the frequency 50 hz 60hz only why not others like 45, 95 56 or anything , why should we maintain the frequency constant if so why it is only 50 hz 60hz?
What happened when the field winding of dc series motor is open?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)