How can calculate ups battery back up time?
Answers were Sorted based on User's Feedback
Answer / bhushan
UPS / Invertor Battery Backup Time =
----------------------------------
Batt Voltage X No.of (Batteries) X Single Battery Ah /
Total Load (Watts) = No.Hours Backup
Example :- 12v X 20(Batteries) X 200Ah (Single Battery)
/ 6000 Watts = No.Hours Backup
48000 / 6000 Watts = 8 Hours Backup
BHUSHAN
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / cree led street light in pakis
thanks for the useful information you people share
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ms
su-kam inverter company saying in a restive load backup time will be battery ah*battery v*80%/total load.(20% is battery
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mana
UPS Bachup time=(Battery AH*No.ofbattery/UPS capacity in
kva*130)*60=mins
| Is This Answer Correct ? | 9 Yes | 9 No |
Answer / chesda
T = (N.Q.eff.PF.V)/Load
T : Backup time [h]
N : Number of batteries [Nos]
Q : Batteries charge [AH]
eff : Inverter efficiency [%]
PF : Load power factor
V : Batteries voltage [V]
Load : Connected load [W]
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / tapas
UPS Battery Backup time= (No. of battery X Volt per battery X Battery AH)/ Load in VA
(No. of battery X Volt per battery X Battery AH)
Backup = ------------------------------------------------
time Load in VA
Note: KW should be converted to VA before applying the formula
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / basanta das
Ups Standard Bacup Time = (Battery Volt X Each Battery Ah X No. Of Batteries) / load in VA
For example: Volt 12 x AH 26 x Total batteries 16 = 4992
Now divide the above with required load (1 KVA) =1000VA
So result is 4992/1000 = 4.992 hours
Means your UPS will run for 4.992 hours in standard calculation method, but in actual there will be a UPS energy waste or dissipation, let your UPS efficiency is 80% then you will get actual time
4.992 x 0.80 = 3.9936 hours i.e approx. 4 hours of backup time for 1KVA load if you have 12volt, 26AH battery of 16 nos.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sudarshan
i hv 600kva ups
how many batterys required
with formule
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / akshay kumar
UPS BACKUP TIME=CONNECTED LOAD/(BATTERY VOLTAGE*NO. OF
BATTERY)
SUPPOSE CONNECTED LOAD = 1KVA,BATTERY VOLTAGE=12,NO OF
BATTERY=2 THEN
BACKUP TIME =1000(1KVA)/12*2
=1000/24=41.67 AH
(IT MEANS BATTERY DISCHARGE CURRENT =41.67 AH IN ONE HR.)
IF YOUR BATTERY CAPACITY IS 150 AH THEN
BACKUP TIME=150/41.67
=3.35 HRS (APPROX)
| Is This Answer Correct ? | 4 Yes | 5 No |
what is the minimum pay scale for electrical engineer (building construction)in kuwait? plz revert back with yrs of experience & pay scale respectively.
What may be happen if neutral and earth is shorted in a substation
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING) I O (current operating)?
what is interfacing in computer studies?
What is resolution of a measurement?
How to improve insulation resistance of Motor
1.What will be stored in online ups EPROM IC?
why can tv operate at low voltage??
what is the meaning of DY-11 Z-5%
what is the essential resistance of r y b phase short citcuit ? Eg in star connection we doing this kind of short circuit oly
whose motors self starting synchronous or Induction motor?give fact reason why not self starting another mother
what is the long transmission lines
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)