some practicle study shows that the reactive power at the
receiving end is not equal to the reactive power at the
sending end.But according to theory the reactive power is
exchanged by different parts of the network – capacitors
and reactors permanently, but is never consumed or produced.
Then Where that reacrtive power loss occuring?is there any
formula to calculate reactive power loss?
Answers were Sorted based on User's Feedback
Answer / blake australia
The transmission lines have a capacitive charge due to the
fact that they run at a distance from ground (at a
different potential. This capacitive effect is absorbed by
other parts of the network
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mahesh bial airport bangalore
Dear BLAKE thank you for your answer and your answer is
really good but reactive power loss nothing but a voltage
drop in the line so because of this voltage drop & losses
sending end power will not be same in the recieving end &
once again thak you for thisquestion sender
| Is This Answer Correct ? | 0 Yes | 1 No |
hai friends i have BSNL JTO exam on next month so if any body have model question paper or give preparation tips to my mail id kumar4486@yahoo.co.in this will helpfull for my future .plz & thank u by kumar
What should be the voltage between neutral and earth of a UPS?
How many methods to take IR value of Current Transformer?
DOES AN EARTH FAULT CURRENT ON THE DELTA SIDE OF A 6.6/33KV STEP UP STAR-DELTA CONNECTED TRANSFORMER REFLECT ON THE STAR SIDE? IF YES, THEN HOW AND WHAT IS THE AMOUNT OF CURRENT REFLECTED?
What is the safe limit of voltage between earth and neutral in india.
2 Answers Incepta Pharmaceuticals,
Hello friends., my question is related to testing of current transformer... A Ct having knee point voltage of 750 volts., and I have two step up transformer's of rating 230 v to 440 volts., can I obtain the value of 750 volts by using the two transformer's.... If yes then how could I connect the transformer's to obtain knee point voltage?? thank you in advance
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
What is the difference between voltages or potential difference? And what are they?
When VFD is connected to a 3 phase main supply there is load current difference between incomer to VFD and outgoing from VFD.
We have a bank capacitor rating of 60 KVAR for a overall load of 160 KVA and we have connected three loads of 50KVA each. We would like to auto matically correct PF using APFC. How do we design it?
what is the formula of knowing the clabe size on any load?
I need the recommended size for a 3 phase transformer at 13.8 KV Primary and connected loads of 3000 kVA at 4200 volts and 2375 kVA @ 480 volts AC.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)