We have a bank capacitor rating of 60 KVAR for a overall
load of 160 KVA and we have connected three loads of 50KVA
each. We would like to auto matically correct PF using APFC.
How do we design it?
Answers were Sorted based on User's Feedback
APFC panel should be connected to main incoming busbar i.e.
from where 160 kva load was fed. 60 kvar capacitors should
be devided into smaller capacities i.e you have to use
either 6x10 kvar or 4x 15kvar or 10x6kvar. I will consider
6x10 kvar. in APFC you have to programe each stage
capacity. here the value is 10 kavar. You have to take 6
no. of capcitor switching duty contactros and to be wired
as per the APFC. It also requires one CT signal and voltage
signal(any one of the three phases of main busbar). You can
program s/on and s/off time in APFC. and also you can
program target power factor. EPCOS apfc is the best
controller I have used.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / yuvraj gaikwad
devide the 60kvar capacitor into 4 or 6 banks of 15kvar or
10 kvar.use apfc relay of 4/6 stage which wil automatically
switch the cap banks to achive the target power factor.
The apfc i suggest is SYCON apfc which has more features
and available in diffrent models with fifo as well as
intelligent switching.visit website www.syconindia.com
| Is This Answer Correct ? | 3 Yes | 2 No |
What is the inside of ACB & VCB & SF6 breaker's pls tell me about this
in cvt,there are two windings,1a,1n and 2a,2n.in my one project i use only one winding i.e.1a,1n. the other winding is not in use, so i connect it in open delta and want to close it by ibsertibg thermal resistor. the output of cvt is 132kv/115/sqrt3. plesae tell me exact value of resistor, so i may close it to avoid the resonance phenomenin. send me answer on this email adress please. aetcon-po@aetcon.com
Why we use two wattmeter during block rotor test and no load test of 3phase induction motor? And how can we understand the neat power requirement of from this test?
what is pmu
I am shobana from Chennai. I am having my personal interview on 19th Dec at Chennai.kindly mail me the questions to mail id shobana.shanthi@gmail.com
how can we know the size of cable cross-section from current rating ?
can we connect transformer with star conected secondary to delta connected primary in series?
why ct's&pt'S out put called as burden,why compelsary short ckt the secondary of ct's while removing the burden?
how point on wave controller works.
we specify current in case of feeder but in case of distributor voltage, why?
What is effect of power factor on change in voltage
13 Answers APNPDCL, apspdcl, My Home Industries,
What are the types of class b amplifier?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)