APFC panel should be connected to main incoming busbar i.e.
from where 160 kva load was fed. 60 kvar capacitors should
be devided into smaller capacities i.e you have to use
either 6x10 kvar or 4x 15kvar or 10x6kvar. I will consider
6x10 kvar. in APFC you have to programe each stage
capacity. here the value is 10 kavar. You have to take 6
no. of capcitor switching duty contactros and to be wired
as per the APFC. It also requires one CT signal and voltage
signal(any one of the three phases of main busbar). You can
program s/on and s/off time in APFC. and also you can
program target power factor. EPCOS apfc is the best
controller I have used.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / yuvraj gaikwad
devide the 60kvar capacitor into 4 or 6 banks of 15kvar or
10 kvar.use apfc relay of 4/6 stage which wil automatically
switch the cap banks to achive the target power factor.
The apfc i suggest is SYCON apfc which has more features
and available in diffrent models with fifo as well as
intelligent switching.visit website www.syconindia.com
| Is This Answer Correct ? | 3 Yes | 2 No |
Size of the power cable like 1.5,2.5,4 sq.mm which area calculated from whick area or how specified the size?
what kinds of Transformer oil grade is better for power transformer ?
How can we increase fuel-power ratio of any DG set?
how to find out capacitor range?
how is motorized megger operate?
what is the need of representing AC power in sinusoidal waveform? why not in square or rectangular etc...
How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?
what is the difference between droop mode and ischnorous mode in thermal powerplant?
if flux and load static in dc motor and supply voltage increases 20% then what happened in speed
What is the meaning of BREAKING and MAKING CAPACITY in case of CIRCUIT BREAKERS.
why we connect the capacitor bank in star , not in delta in any system
What is the resonant peak?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)