i have 28/32 MVA power transformer with 11/6.6 KC voltage
rating and 12%impedance.it have star connection at both
side.but it have another thied winding tertiary
winding.what is used of this winding.
pl tell me
Answers were Sorted based on User's Feedback
Answer / manish meena
tertiary winding used for,
-to obtain additional voltage
-to stabilize neutral in case of star/star transformer
-to reduce third harmonics and control zero sequence
impedance.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / jnanesh
In star connected trans. third hormonics is significant so
to reduce that effect it is used.In delta connected trans.
third hormonics circulate witin and there is no effect.
Also plz note that in some substation for feeding internal
power to substation or local area this additional winding
is used.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ajay patel
How your tertiary Winding is connected? what is the rating?
If all three phase terminals are bruoght out then it can be
used as additional seondary winding. But If this tertiary
is connected in Open Delta & 2 termianls of open delta
brought our for Earthing. That means this is installed for
Harmonic purpose. If you have rectifier, Big VFDs or such
load which can generate Theird Harmonic in big amount then
these third harmonic can be reflected in entire Grid, if
your transformer is Star - Star. Which is may damage other
equipments / consumers also who are connected with same
supply. Hence it is necessory to control 3rd harmonics in
grid. For this you can provide Delta Primary for
Transformer. But you dont have delta in primay tehn you
have to provide Tertiary winding with open Delta. This Open
delta is closed out side of Transformer & Complete Delta is
formed. This Delta winding should be earthed to minimise
harmonic disturbance in the system. Please check, do you
have earthed tertiary? Is it in Delta?
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / manish jauhari
Any unbalanced loads, results in increased cirulating
current with in tertiary Delta winding, thereby keepinng
pri & sec voltages with in limits.
| Is This Answer Correct ? | 2 Yes | 2 No |
Hi Paliwalsureshi,
Makers of such transformers usually provide a tertiary
winding connected in delta. This winding is sometimes called
compensating winding. As others have rightly said this
winding help to eliminate the harmoics which may interfer
with communication in power system. Before the advent of
microprocessor-based differential relays the old
differential scheme with star-star on one must have a delta
winging in between.In a nutshell any star-star connection
must have a delta tertiary.
| Is This Answer Correct ? | 0 Yes | 1 No |
in alternator what is use of AVR ? how AVR is operating either AC or DC?
what type of cables exsisting in the world and how many types
hi, i have 3x200KVA and 2 x 80KVA UPS with battery bank of 150AH 68Nos. and 100AH 204Nos., i need to install AC either ductable or PAC type, so can you help me to calculate heat load and capacity of the AC to install.
A 400 V, 50 Hz, Δ connected synchronous generator has a field reactance of 0.1 Ω and armature resistance of 0.015 Ω. At full load, the machine supplies 1200 A at 0.8 pf lagging. Under full-load conditions, the friction and windage losses are 40 KW and the core losses are 30 KW. What is the machine’s overall efficiency? Ignore any field circuit losses.
What will be the resultant out put voltage when two different voltage rating batteries are vconnected in parallel? pls. answer with example if available.
when transformer oil should be filtered/tested?
Dear sir, I am working in wind mill division , pls explain Pls explain in details with formula My question is Wind speed 3.5 M/s Gen RPM is 1500 ( 25 K/w Production ) Wind speed 12 M/s Gen RPM is 1500 ( 220 K/w Production ) Why in 3.5 m/s generation was low , why in 12 m/s generation was high , Pls dont explain wind force or wind density , that one already i know For the above question RPM was same why the KW was different Answer : 1. Its depends on the density ( Force ) of the air Sir , Pls explain wit Formula sir
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
What is the current carring capacity of 0000SWG and 0SWG overhead solid bare copper conductor. If possible please provide reference for various sizes Vs current ratings
how choose conductor &caple&wire depending upon the load
how to calculate busbar size? if ex:1000amps i need to calculate busbar size and what size of bar?if any example caculation pls give the formulas.
can we increase our frequency rate in INDIA?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)