we have one ups its neutral is not earthed.its one
distribution MCB has a earth fault.but we can not put off
any MCB.so how to find out that in which circuit is earthed
without isolating the breaker.
Answers were Sorted based on User's Feedback
Answer / dudeblore
By using a megger meter you an find out the faulty circuit.
The faulty circuit will have a less resistance as it has
connected to earth somewhere.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / guest
measure+ve to earth the earthed mcb will show low voltage
than other mcbs
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / sumitgarg
to aviode that probelem in furure you can use a ELCB or
RCCB that will help to find and earth the earth fault
current.
that shoud be of 1 Amp. rating.
| Is This Answer Correct ? | 0 Yes | 3 No |
acb(AIR CIRCUIT BREAKER)NOT CHARGING AUTO
Re: how to calculate diesel consumption of a D.G.Set? Answer # 1 We can not calculate the diesel comsumption...depending upon load it will conume the diesel...suppose the 1500kva D.G is running and the load is 1000kw means it will consume 150-200 liters per hour....
How we can change the direction of rotation of Induction motor? Prove it using graphical methods.
if transmission voltage expressed as the multipple of form factor(1.11)........11,33,66,220 etc......then why madakkathara substation(kerala) voltage is 400kv..not 440.....?
1.What is effect of capitance in transmission line? 2. After raising the voltage at receiving end what will be happen? 3.how we nullify or control the raised voltage at receiving end?
Draw the wave shape of armature current in a generator subjected to a sudden three phase short- circuit at its terminals. Define various reactance of generator from this wave shape.
Why have the transformer one earthing to their neutral? Why have the transformer many earthing to their body?
What is cathode ray oscilloscope (cro)?
how to calculate the MF in meter reading
what is the difference between servo voltage stabilizer and general voltage stabilizer?
What are the section criteria for cables. Now everywhere XLPE power cable is used or PVC is also used?.
Which level of the Transformer oil got dielectric strengh? And why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)