What will be the effect of in HT XLPE 220 KV
cable when one side of the Armour/cable ends are not
grounded. Will there is difference between 3-phase voltages?
like: if
A. Both End of Cable grounded Phase Voltages:- V1=219 KV,
v2=220 Kv, v3=220 KV.
B. One End is grounded other is not: than Impact on Phase
Voltages:- V1= KV, v2= Kv, v3= KV. Remain same or
unchanged??
Answers were Sorted based on User's Feedback
Answer / hemant
mostly we consider that armour is given for machanical
protection to cable from any type of hard punching on cable
and other if cable get damaged then it touch to armour
which alredy connected to ground hence our differantial
reley get pick up and device which connect to ht cable is
protected. if both end of armour is connected to ground
there may not any effect to supply voltage in cable it
depend upon cable insulation. only leakage current get
discharge via armour to ground. hence in point of me trere
is no one effect on 3 phase voltage it also remain same.
one thing is that armour one end require to connect ground
and second to device for earthing to device.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mahendar kumar
In my opinion Phase voltage would be affected due ungrounded
one end cable.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / k.prakashchandra
You have measured voltages with the help of PTs located near
the earthed cable ends . As there is a slight difference in
capacitances of the three cables to the Armour(probably due
to unequal lengths) and impedance of the PT is higher than
that of capacitance of the cable ,the neutral is decided by
the capacitances.There is no difference in actual voltages
but there will be a slight difference in measured voltages
Is This Answer Correct ? | 0 Yes | 0 No |
What is trickle charging system?
can we synchronize star system generators with delta system generators?
what is high voltage in india?
IS diode and blocking diode are the same?..what is meant by blocking diode
Why do you have to use Protecion relay with the function MTB ( Mechanical Trip Button ) for electrical system.
Why arc quenching is used in Diode ?
WHY THE RATINGS OF TRASNFORMER IS IN KVA?
Why are the laminations insulated from each other?
Two bulbs of 100w and 40w respectively connected in series across a 230v supply which bulb will glow bright and why?
what is the rating of Insulation tester for measure 15 KW, 3 phase 415V 50 HZ induction motor?
what is the use of back emf?
Why Parallel operation of two Transformer are Required?