for testing busbar (33kv) hi-pot .whether we can apply DC r
not.and what is the test volt for that .explain
Answers were Sorted based on User's Feedback
Answer / senthil kumar
we can able to test ac or dc. thats manufactures chosen.in ac hi-pot leakage current will be more(mA).but DC hi-pot leakage current will be less. but dc voltage charge the capacitance. in ac hi-pot we are applying 2V+1X 0.8 in dc hi-pot 2V+1X1.414X 0.8.
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / vijay
Yes, we can.
For test voltage we have to apply 80% of factory test
voltage i.e. 80% of 70 kv ac (factory test voltage) =56 kv
for 1 min.
Is This Answer Correct ? | 11 Yes | 6 No |
Answer / shaikh
For 33KV Ac Busbar testing, we can apply 5.0k (5000v)DC for
1-3 mints.
Is This Answer Correct ? | 3 Yes | 10 No |
Answer / ashish
For Testing Busbar 33 Kv ( HI-POT ) We Have To Apply the (
1.732* 33000)DC Volt for 3 min.
Is This Answer Correct ? | 9 Yes | 18 No |
motor is 12.5hp after starting few minets motot get hot? why?
What exactly is meant by harmonics and harmonic current?? and what is skewing with regard to this??
Explain the operation of variable frequency transformer?
Why transformer, generator, ups rating kva?
Types of circuit breaker
if a 2 ohm resistor,2 ohm capacitor and a 2 ohm inductor is connected parallely to 12v source.Then what is the value of current in each branch.Is current flows in each branch at the same time?If not so then provide the proper sequence
What is the difference between bushing and insulators.? what is the creepage distance?
capacitor is load free component but why ampare meter shows current when capacitor bank breaker close?
why do you give the dc supply to field of alternator
how the speed of the gets motor regulated. does it draw the same current on the all speed level.
why we use four type of phase angle difference between pimary & secondry winding of a transformer & where we use them?
How many distance in distribution pole OR 33Kv line pole