How can we calculate the fault level of the distribution
system knowing the percentage impedance of transformer &
subsequent equipments.
Answers were Sorted based on User's Feedback
Answer / mbao richie
simply means the bus rated at that fault level can
withstand the electrical pressure(voltage) for which it is
designated for that period of time
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srikanth
Dear friends,
in the above calculations people consider the % impedence
but they are not calculate the fault impedence to get MVA
of transformer.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / jigar shah
suppose transformer (11 KV/433) is of 1000 KVA & %
impedance is 4 .LT side Fault level can be calculated as
below :
KVA = 1.732 X V X I X Cos Phi - PF assumed : 0.95
LT Rated current (I) = (1000 * 1000)/(1.732*433*0.95)
= 1481 A
Fault current on LT side = FLC * 100/(% impedance)
= 1481 * 100/5
= 29.62 KA
| Is This Answer Correct ? | 44 Yes | 54 No |
Answer / laxminarayan
suppose transformer (11 KV/433) is of 1000 KVA & %
impedance is 4 .LT side Fault level can be calculated as
below :
KVA = 1.732 X V X I X Cos Phi - PF assumed : 0.95
LT Rated current (I) = (1000 * 1000)/(1.732*433*0.95)
= 1481 A
Fault current on LT side = FLC * 100/(% impedance)
= 1481 * 100/5
= 29.62 KA
| Is This Answer Correct ? | 14 Yes | 46 No |
What is an Isolation Transformer? Where it will use?
is EEE eligible for getting electrical supervisor certificate ? if yes then from which state i sud apply
Why Exciter higher ferquency ?
How to check the thermocouple is correctly connected to cable for K type? (i,e positive pole is connected to non magnetic conductor and negative pole is connected to magnetic conductor)
How to calculate current carrying capacity of copper conductor _ such as cable size 25sq mm,50 sq mm, 75 sq mm, 100 sq mm
A 4-Pole D.C. Generator has a speed of 1500r.p.m. Then what will be the frequency of D.C. Generator ?
role of shunt coil in circuit breakers
which is better 50 HZ supply or 60 HZ supply?
Why inductors are installed in electrical circuits?
As we know that during saturation test of CT from secondary side, the current in secondary shoots up after core saturation. How core saturation effects the secondary current?
A T-T transformer can not be parallel with transformer A V-V B star-delta C star-star D delta-delta
If you see the HRC fuse name plate. Its shown ampere rating shown which is in many KA (like 80KA and so on). any body explain what is meaning of this value?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)