HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF
IMPROVEMENT?
EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?
Answer Posted / girish kumar samal, hindalco,h
as pf not giving ,taking pf 0.8
let pf of load =0.8
kw of load= 65 hp=65*0.746=48.5kw
kva =48.5/0.8=60.625kva
kvar =sqrt(60.625^2-48.5^2)=36.375kvar
if we want to improve pf to 0.95 then
improved kva= 48.5/0.95=51.052
improved kvar= sqrt(51.052^2-48.5^2)=15.9411
requard capacitor range = 36.375-15.94=20.43kvar.
| Is This Answer Correct ? | 26 Yes | 12 No |
Post New Answer View All Answers
What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention
Which type of air compressor is used now a days in the market. Keeping in mind of energy efficiency and maintenance points. Relevant documents may also be sent on mentioned email ids.
my diploma certificate in my higher education college
WILL SCHNEIDER MAKE ACB(MASTERPACT)TRIP ON REVERSE POWER?
what is power factor ? how we can calculate the low power factor and amount of capacitor for improve that low factor ?
critically criticize the application of ring main unit in power system
Why synchorised generators are used for the production of electricity?
Why High voltage are generate noise ?
What will be the current drawn by HT motor, if low voltage is applied.. any formula to calculate the LT amps of HT motor.?
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
how can we make cable shedule for controll wiring ? which details must be required for it.?
what is die electric strnth of transformer ?
please send me privious exam's queation papers of section engineer(electrical).
What is real time power factor control panel(RTPFC)?
In single phase capacitor motor, if the motor rotate reverse direction then how much power will be consumed by the motor and why?