how to calculate the no. of turns in secondary side of CT?
Answer / jdp
Basic trafo amp-turn is I1N1=I2N2
CT ratio 100/1 so I1=100, I2=1
in case of bar primary
N1=1
SO N2= 100*1/1 = 100 turns
in case of wound primary
N2/N1=100/1=100
so in this case we must have information about N1 primary
turns to find out Secondary turns of CT N2
Is This Answer Correct ? | 7 Yes | 0 No |
In CT,which terminal(s1,s2) need to be grounded?
What is the difference between double compression
7 Answers Bhel, Hyundai, Orchid Chemicals and Pharmaceuticals, PDO, Prefamac,
WHAT ARE THE DISADTAGES OF SINGLE-WIRE-EARTH-RETURN SYSTEM USED FOR RURAL ELECTRIFICATION?
Difference between hopkinson and swinburne's test
Why SF6,VCB,Oil Ckt Breakers are use in HT Side need brief information ?
what is ups?how its works?and what is there in static switch how it works?
What is the basic difference among IPS,UPS,EPS?
Why electrical engineer use Cu Strip for transformer neutral why not GI Strip? What if we use GI instead of Cu does it affects the transformer performance.
Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three numbers of 1250KVA ,11KV/0.415KV Transformer to feed the Factory load. We have found some abnormality. In one of our Transformers the leakeage current from transformer body to earth through earth continuity wire is almost 86 Amp but in other transformer it is (5-10)Amp. where the load current on three phase and neutral are respectively 1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical person help me about the reasons of this situation and how I can rectify the fault. Moreover,I have measured the earth resistance of the Earth continuity wire which is less than 1 Ohm. Thanks Tapas Barua
What is various types of electrical formula?
reason of diode failure in alternator
how tubelight circuit is connected and how it works?