how to control the generator output voltage?
what r the condition should satisfy for synchronization?
Answers were Sorted based on User's Feedback
Answer / rajkumar r
By varying FIELD excitation we can control the output of DG.
Practically by changing AVR setting we can control the
output of DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. Speed/frequency should be the same
4. Load impedance should be the same.
Is This Answer Correct ? | 27 Yes | 3 No |
Answer / rvg.msceb
to be very clear, in commercial generator, nobody using
separated excitation system. self excitation is the best
method unless some specific reasons.
For controlling output voltage, a device called AVR,
automatic voltage regulator to be used, and it sense the
output voltage at each instance, and adjusts accordingly.
these are the condition for syncronization.
1.phase sequence of both generators should be same.
2-frequency shuld be same.
3-terminal voltage shuld be same.
4.both generators should have nearly same percentage
impedence.
Is This Answer Correct ? | 24 Yes | 1 No |
generator out put voltage is controlled by varying
excitatoin.
for syncronising of generator :
1 phase sequence should be same
2. voltage and frequency should be same and one most
important
3. phase angle should be same
Is This Answer Correct ? | 17 Yes | 4 No |
Answer / prembujju, park institutions
To control the output of the generator we have to consider the
following conditions
1. phase sequence will be same
2.terminal voltage will be same
3.frequency will be same,
if we change the speed of the prime mover we can get
controlled generator output. but fuel input increases which
changes the frequency also. so system not matches for those
three conditions.
on other hand the output of the generator can be
controlled by increasing or decreasing the excitation
depending of the load demands.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / pravesh
By varying FIELD excitation we can control the output of DG.
Practically but commertial d.g. sets are controlled by self
excitation and avr controls the output voltage output of
DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. frequency should be the same
4. percentage impedance should be the same.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / pavan
By varying the turbine speed. voltage, frequency & speed are
to be consider for synchronization.
Is This Answer Correct ? | 5 Yes | 19 No |
Answer / pradeep kumar rawat
by contoling the fuel we can contol the output voltage of
generator.
condition for syncronization.
1-phase sequence shuld be same.
2-frequency shuld be same.
3- terminal voltage shuld be same
Is This Answer Correct ? | 3 Yes | 24 No |
What is the Difference Between MCCB & ACB & VCB
neutral carrying current more than phase in 3phase supply.i want to know the reason?
What is expand formation of AYFY cable
IF 5000amp current on LT 440V. then how much it will draw amp on HT 11KV side
what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then why we are not using in our day to day appliances?please justify the answer
in indoor type circuit breakers why only the corner breaker trips specially during cold season. What is the reason.
why in the three pin plug all 3 pins are cutted ?
what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm
what's mean by Transient stability analysis?
what are the settings is there for ABB REM543 Generator Protection Relay
An alternator is started without excitation then how much voltage it will produced at strating at full rpm??
what will happen if any motor runs long time with star connection in400vA.C. system