What is the function of earthfault relay?
Answers were Sorted based on User's Feedback
Earth fault relay is a relay which is sense the faults
between the phase and Earth (not b/w neutral to earth)
| Is This Answer Correct ? | 152 Yes | 29 No |
Answer / micro power system, bangalore.
Actually earth fault relay's function is,it calculates the
vector sum of all the three currents flowing in R Y B
lines. If the vector sum is not zero then there is a fault
current flowing in particular line. since these lines are
connected to load say generator then, more than the rated
value of current flowing through windings ,hence windings
will damage so to prevent these type of damages EFR is
used.
if any comments pls send to shreeshara@gmail.com
| Is This Answer Correct ? | 123 Yes | 18 No |
The function of earth fault relay is to to protect the
device from earth fault. there are 2 types of earth fault
fault relays
1.neutral ct conneted earth fault relay. it will sense the
current flowing through neutral while earth lerakage.
2.three phase ct's connected earth fault relay.in normal
condition the sum of three phase ct's current in zero.
when earth fault the sum of the 3 phase ct's curret are un
balanced that time relay acts.
| Is This Answer Correct ? | 67 Yes | 7 No |
Answer / t eswara rao
Function of the earth fault relay is to operate for the
leakage currents to earth. There are two types of earth
fault relays depending up on the configuration
1. Residual current earth fault relay
2. Sensitive earth fault relay
| Is This Answer Correct ? | 38 Yes | 8 No |
Answer / pratheesh
I agree with Mr.Ravikumar except in one point.
If the load distribution of a 3 phase 4 wire system is not
balanced in all three phases, there will be some potential
in neutral wire and thus a current flow also.
In this condition, if the neutral wire touches to earth
after the earth fault relay CT, definitely this E/F relay
will sense this current flow from neutral to earth and thus
trip the circuit.
If any other disagreement, please mail me at
pratheeshtn@gmail.com.
Thank you.
| Is This Answer Correct ? | 33 Yes | 5 No |
Answer / c.venkatesan
1.the earth fault relay funtion is to senses and derived
the current from phase to earth fault
depands upon the ct connections used in the scheme
the earth fault relays are classified
1.residual earth fault
2.stand by earth fault
3.restricted earth fault
4.senstive earth fault
all will be derived the input currents from different ct
connections
| Is This Answer Correct ? | 20 Yes | 4 No |
Answer / madhu kiran.g
earth fault relay is a device used protection.
when an unbalance current flows through the line this relay
operates and trips the circuit breaker.
earth fault relay is used between phase and earth faults..
| Is This Answer Correct ? | 18 Yes | 5 No |
Answer / gova
The E/F relay will operate under unbalanced condition
i.e 1) during earth fault
2)During any phase open (when unbalanced current
exceeds the relay settings)
regards
gova
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / sethurama.
Earth fault relay is sensing the fault between phase to earth and also neutral to earth. When current flowing through earth that time it will be tripped.
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / visaw
earth fault relay operated between two phases for unbalcing
voltages
| Is This Answer Correct ? | 12 Yes | 8 No |
what is the formula to find battery back up of ups?
Yazaki india pvt ltd interview questions qurey related
What are the Return ( Monthly / quarterly/ Annual submitted to Electical Inspector for an establishment (Factory in Maharashtra-- Small scale category having seperate HT line of 22KV ) as per Maharashtra Electricity Act
HOW EFFICIENTLY LOAD IS SHARED BETWEEN ALTERNATORS
i work as a technician at a private company.. i used to take amp reading for certain appliances such as air con.. the problem is when i clamp the neutral, wire there is a current reading.. from my understanding for single phase system neutral should not have current unless if the circuit is not complete.. yet the air con still work
why 3phase is 440v but where as we get phase voltage 220v,we have to get 220*3=660v.can u pleas give in detailed
what is the minimum distance between substation wall and LT panel outer surface?
What is the use of Gateway RTU like ABB RTU 560 in power plant, SAS system ?
WHAT IS counter flux IN CT?
please send me previose rrb junior engineer qustion papers
what is meant by armature reaction?
How to calculate or testing the KW in generator
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)