Answer / soleha sarni
EFR is a relay which it sense fault between the phase and earth. the main function of the relay is to operate for the leakage currents to earth. there are two type of earth fault relays:
1. residual current earth fault relay
2. sensitive earth fault relay
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / arpan goswami
earth fault relay dense the fault if any leakage current
flow through the ground then it send signal to the circuit
breaker and it will automatically shut-down the equipments
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravi kolhe
An earth fault relay is activated by the fault current flowing from line to earth. Earth fault relay continuously measure the current.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bramananthan
Whenever the unbalanced current flow in the circuit the connected EFR sense that current and giving signal to the UV or shunt coil which is placed in the breaker.At that instant the breaker comes to Trip & break the supply.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / irfan
Dear friends EFR and ELCB (Earth leakage circuit breaker) function is same but EFR is used to protect the heavy load or Transformer and ELCB is used for to protect the small load such as domestic load . if any mu friend is disagree with me please point out my fault thanks.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pradhumn singh
It is a relay which sense the fault phase to earth .
| Is This Answer Correct ? | 0 Yes | 0 No |
Earth fault relay is a relay which is sense a fault between earth and phase.
| Is This Answer Correct ? | 0 Yes | 0 No |
does any one know where we can purchase insulation oil for high voltage oil filled cables
What is the purpose of reactor.why we used in over head line?
Why there are some equipment(i.e:TV) that using 2-pin plug instead of three? What happen if there is current leakage? Are we going to get electric shock??
0 Answers College School Exams Tests,
How can we increase the capacity of exixting capacitor bank??????????????? PLS. Help
12.5 tons a/c is their how much kva generator can recommend to the customer.
In radial network the source is fed from 1 end both ends at central
It is observed that AVR of an Alternator is more likely to fail if the Generator and Mains Neutral are directly connected to each other. Why should this be so?
Motor,transformers,capacitor tubelight etc....
what does mean of RCT and STR in diffrential CT?
what is the disadvantage if earth is connected to neutral
What is Neutral Transformer? what is the use of this?
for 644KW load which MCCB should i use
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)