A transformer which offers neutral ,when the neutral is not
available, is called neutral Tr. It is just like a star
connected primary of a transformer of the rated voltage with
or without secondary.The star point can be used for earthing
as well as for using single phase appliances.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / murugan.k
The Neutral transformer is mainly used to reduced return flow of earth fault current to the main transformer winding. It's just act as a resistive path in the Neutral side. Beacause when Earth fault occur in the high voltage line, A huge amount of current flow's through the neutral.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / srikanth
to operate an equippment phase and neutral is necessary.
for phase u have to take where as for neutral by providing
neutral transformer we can use...(simply neutral t/f act as
return path). and use of t/f can be used for small range as
well as large range...
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pappu gore
neutral transformer is used to derive a neutral-to-earth connection for systems that do not otherwise have one.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why does the speed regulating system adopting I controller have no steady-state error? In this single closed-loop speed regulating system, when the input of the I controller Un=0, what is the output voltage of the regulator? What factors do the output voltage depend on?
What is the difference between Derived earth Fault and measured earth fault.How it works.
If a capacitor bank is having rating 750kvar for 6.6kv. Then for 3.3kv how much will be the rating of capacitor bank.
what is tpdt
can we replace d.c.motor by 3 phase induction motor for a particular application
which have higher efficiency transformer or induction moter
what is the differenc between A.C. and D.C, which is more dangerious?
how moving coil indicator works?
What should be setting for alarm,tripping and cooling fan on for power transformer's oil temp. and winding temp. indicator?
WHY THAT THREE COLORS CHOOSEN IN 3 PHASE? WHAT IS MEAN BY RYB?
Are you connected Transformer neutral eathing with it's body earthing or earthing met of switch yard.? Yes or No ? why ?
I have connected 04nos. earthings to a transformer through 04nos. earthing pits seperately. 02nos. earthings are connected to T/F body, and 02nos. earthings are connected to T/F neutral.T/F capacity is 2000KVA, 11KV/415V. But after completing of 02 years successful operation ,we are facing following problems- 1. CT/PT occured blast one time 2. HT cable box occured blast two times 3. One body earthing strip and one neutral earthing strip of transformer are overlapping at some places. Whenever these two strips are pressed at overlapped points, they made spark. What is the reason of spark? Please explain the reason & rectification of above problems
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)